Hi Wrenchers,
I am configuring a 50KW roof array and plan to use a 3 phase 50KW central inverter. There are multiple options for the lugs/fusing for the Inverter incoming DC conductors. PV Powered for example offers everything from a single set of unfused lugs for the Positive and Negative input up to 5 x 60A fused lugs. My question is if I am using a external fused DC string combiner with integrated DC Disconnect and bring the single set of conductors into the inverter with the option of 1 set of lugs with no fuses in the inverter what protects the large conductors between the fused string combiner/Disco and the inverter if there was a problem such as a short on these conductors?
Any and all feedback is appreciated.
Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120227/d7c9d293/attachment.htm>
More information about the RE-wrenches
mailing list