[RE-wrenches] Design Question re Battery Bank Sizing
Ray Walters
ray at solarray.com
Wed Feb 15 18:33:04 PST 2012
Hi Allan;
B&B battery, which I've used for years for sealed battery applications
has excellent charts on discharge rate vs time; just what you need for
your design. I've also found them to have stable voltage under very
heavy loads (electric vehicles) right up until they're fully
discharged. I don't really know about the Concordes.
Ray
On 2/15/2012 10:53 AM, Allan Sindelar wrote:
> Esteemed fellow Wrenches,
> We need to size a battery bank for a GTWB just for starting a well
> pump. The well is on its own meter, so as long as the battery voltage
> does not crash when the pump starts there will be plenty of capacity
> left over for minimal loads. We'll be using sealed batteries, most
> likely Concorde SunXtenders. According to theSunXtender Technical
> Manual, Concordes can handle up to a C/0.2 charge rate (500A for a
> 100Ah battery), but there is no discussion of maximum discharge rates
> or voltage drop due to large surge loads.
>
> The pump is 3HP and is conventional 3-wire, not soft-start. The well
> is 940ft. and the depth to water is unknown. It pumps into a pressure
> tank, not open discharge. Customers are not interested in replacing
> the pump, but might be talked into adding a soft start Franklin
> controller, although at this preliminary design stage we're not
> certain one is available for this particular model. The inverter would
> be a Radian, so system voltage is 48V.
>
> I would think that configuration would make a difference, as well as
> size. Using 12V batteries in series/parallel would minimize
> interconnect and terminal resistance. I think that it would also allow
> multiple paths for discharge current, reducing the voltage dip.
>
> What's your best guess at the smallest size battery bank that would
> reliably start this pump, and how would it best be configured?
>
> Thank you,
> Allan
>
>
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120215/b45dec40/attachment.htm>
More information about the RE-wrenches
mailing list