[RE-wrenches] SolarEdge v Enphase

Darryl Thayer daryl_solar at yahoo.com
Fri Jan 13 17:47:52 PST 2012


I have like many of you installed both micro inverters and solar edge optimizers.  We have had failures on both, both Co's have been very quick to respond.  


For installation the optimizers were a lot faster than the micro's to install, nothing is a fast as a string inverter.  I am sold on the optimizers, as I see improved performance under shade conditions.  I have two more optimizer system on the books for spring, and will be able to comment.  

DT



________________________________
 From: Marv Dargatz <Marv.Dargatz at solaredge.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org> 
Sent: Thursday, January 12, 2012 6:46 PM
Subject: Re: [RE-wrenches] SolarEdge v Enphase
 

Dan,
 
Thank you SO much for that post.  You are absolutely right on.
 
EVERY component in a circuit can be the weak link.  Component quality, design margin, and actual use conditions really dictate what is going to fail, and when.
 
 
See ya!
 
Marv
Director of Technology and Support, North America
SolarEdge Technologies, Inc.
Tech Support North America:  +877.360.5292
Mobile: +530.392.0356
 
From:re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Thursday, January 12, 2012 3:59 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge v Enphase
 
Wrenches,

I wish this urban myth about electrolytic capacitors would
die, but it won't.  It's been a wonderful marketing ploy for
some time now.

Simply stated, existence of electrolytic capacitors in inverters
does NOT mean the inverters are less reliable.  Satellites
have been using electrolytic caps for decades, and look
how long THEY last!  (I know, because I've helped to design
power supplies for aerospace applications.)

What it boils down to is this: if a quality electrolytic capacitor
is used within its specifications, you can expect 60+ years
of life from it in an inverter application.  Conversely, if a
circuit is poorly designed, you can ruin any electronic part
in a very short time.

What defines capacitor "life"?  It's defined as the doubling
of the internal effective series resistance of the capacitor
from the value it had when it (the cap) was new.

This is energy lost.  It also causes the capacitor to operate
at a slightly higher internal temperature than when it was
new (all other factors being the same).

Result?  It all depends on how the circuit is designed.  In
our case, the inverter efficiency decreases approximately
a quarter to one half of a percent.   The waveform distortion
also increases, but it takes lab grade equipment to detect
the change.  If you're worried about a 1/2 percent drop in
the inverter efficiency, your concern is misplaced.  After all,
PV degrades over time much more than that!

So why the bad rap on capacitors?

Like tires, they DO wear out.  40 years ago, "premium"
tires were rated for 30,000 miles.  Could you wear them
out in less?  Absolutely!  Drive like a 16 year old kid with
a muscle car, and it's easy.  On the other hand, I just bought
a new set of tires.  The old ones still had tread, but at 88,000
miles, they'd seen their better days.  This is a far cry from 30k
mile tires.

Capacitors have progressed in the same manner.  A long time
ago, capacitors wore out in 5 to 10 years.  Today, it's an entirely
different story.

As long as the circuits in which the electrolytic capacitors are
used are well designed, you have nothing to worry about.
Electrolytic capacitors in a well-designed application will outlive
all of us.


Dan Lepinski
Senior Engineer
Exeltech


From: Andrew Truitt <atruitt at gmail.com>
Subject: Re: [RE-wrenches] SolarEdge v Enphase
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Thursday, January 12, 2012, 12:25 AM
 
Does anyone have any experience installing SolarEdge?  The advantage that I see over microinverters from a reliability standpoint is that the power optimizers do not contain electrolytic capacitors.  The inverter is also supposed to last longer since it does not handle the MPPT duties so the electronics are less complex.
 
Marv - Do you have any SolarEdge reliability and / or performance data you can share beyond the white paper on the SolarEdge website?  Also, one issue that I've had with Enphase is an occasional loss of data transfer between inverters and the monitoring system - does SolarEdge have that issue?  If not, how have you overcome it?  Can you share a link to a live SolarEdge system monitoring interface?
 
 
 
Andrew Truitt
Truitt Renewable Energy Consulting
 
 
On Thu, Jun 9, 2011 at 12:40 PM, Mark Frye <markf at berkeleysolar.com> wrote:
Indeed.....
 
Yes it is 1v per module when not operating, but still >250V when operating. That means that all code requirements for >250V still apply to the DC wiring such as bonding bushings for conduit as required etc.
 
SolarEdge is making hay off of this safety feature, but this feature is inherent in microinverters as well. 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com  
 
 

________________________________

From:re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Thursday, June 09, 2011 10:54 AM
To: Wrenches
Subject: Re: [RE-wrenches] SolarEdge v Enphase
Mark, 
I thought that the SolarEdge reduced the 'string' voltage to 1V per unit/module, reducing the high DC voltage risk factor, until the inverter switch was turned on?

The fact that by hitting the "off" switch on the inverter will reduce the potentially high DC voltage to 1V per unit/module could be an advantage from a safety perspective (maintenance, firemen/utility workers)
 
Labor/time-wise, it is like installing both a microinverter system and a string inverter system together, soooooo....
 
benn

DayStar Renewable Energy Inc.  
benn at daystarsolar.ca
780-906-7807 
HAVE A SUNNY DAY 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


 

-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org 



************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer viruses.
************************************************************************************
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender. P  Please think of the environment before printing this email



************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer viruses.
************************************************************************************


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120113/257374da/attachment.htm>


More information about the RE-wrenches mailing list