[RE-wrenches] Request for Gennie Recommendation

Kent Osterberg kent at coveoregon.com
Mon Jan 9 20:26:51 PST 2012


Allan,

I've got a customer that runs 5 or 6 Onan LP generators, all in the 20 
to 40 kVA range, for multiple ranch buildings. Lots of hours with very 
little trouble. The 20-kW is a little bigger than you are looking for, 
but I suspect it would be worth it in the long haul. The smaller ones 
are air cooled.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 1/9/2012 7:59 PM, Allan Sindelar wrote:
> Wrenches:
> We have cautiously agreed to take on a substantial upgrade and 
> rehabilitation of a poorly designed 48V off-grid system. Our upgrade 
> will include a substantial array addition, battery replacement, and 
> charge controller/safety disconnect replacement. But the immediate 
> need is for a generator. The 6 year old system has worn out two Onan 
> residential standby generators; the second one just now (at winter 
> solstice) has failed completely.
>
> We expect to keep the two SW5548 inverters. The site is at 7,800' 
> elevation. The fuel must be LP. The customer is willing to pay for a 
> high-quality unit. We expect only to specify or recommend the unit, 
> but not resell it, so there's no profit motivation involved; we just 
> want the best solution..
>
> I am looking for recommendations of a low-speed, liquid-cooled, 
> commercial- or industrial-grade LP generator, of at least 12kW and 
> preferably around 15kW, with a good reputation for long-term 
> reliability, and that is not designed for home standby use (with 
> phantom-load heaters and controls). It will be located outdoors, so 
> must have a weather enclosure.
>
> I occasionally am asked to answer this same question by Home Power 
> readers, who assume I know the answer because I wrote a primer on 
> generators for HP awhile back. Truth is, I don't have any good 
> recommendations in this size range, and I'm really hoping that some of 
> you experienced off-grid Wrenches who have done larger systems can 
> help here.
>
> Thank you,
> Allan
> -- 
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
> *
> *
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120109/ca59eb5d/attachment.htm>


More information about the RE-wrenches mailing list