[RE-wrenches] battery venting; Corrosion

John DeBoever jdeboever at trojanbattery.com
Thu Jan 5 16:18:34 PST 2012


Hello Wrenches,



Here are some very general guidelines on the subject for consideration:



o   Free flow ventilation is required within lead acid battery room / enclosure:

Batteries produce Hydrogen during charge, depending on the specific design and application

The gassing appears approximately around 80%-90% SOC, depending on the specific design and application

The amount of gassing increase with the battery ageing

Hydrogen becomes explosive at a concentration of 4%

Hydrogen levels must be kept below 1% or 2% percent

Flooded batteries typically produce .418 Liters/AH of Hydrogen at STC, depending on the specific design and application

VRLA batteries typically produce .004 to .013 Liters/AH of Hydrogen at STC,  depending on the specific design and application



o   Cleaning maintenance guidelines:

Batteries are attract dust, dirt, and grime. Keeping them clean will help one spot trouble signs if they appear and avoid problems associated with grime.

1. Check that all vent caps are tightly in place.

2. Clean the battery top with a cloth or brush and a solution of baking soda and water. When cleaning, do not allow any cleaning solution, or other foreign matter to get inside the battery.

3. Rinse with water and dry with a clean cloth.

4. Clean battery terminals and the inside of cable clamps using a post and clamp cleaner. Clean terminals will have a bright metallic shine.

5. Reconnect the clamps to the terminals and thinly coat them with petroleum jelly (Vaseline) to prevent corrosion.

6. Keep the area around batteries clean and dry.



Hope this help,



John


John F. DeBoever
Global Projects & Technical Director - Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Fax: +1-562-236-3239
jdeboever at trojanbattery.com<mailto:jdeboever at trojanbattery.com>
www.trojanbattery.com<http://www.trojanbattery.com/>
[Description: Description: Description: Description: C:\Users\ecastro\AppData\Local\Microsoft\Windows\Temporary Internet Files\Content.IE5\0VK735AY\MC900116474[1].wmf]

    Happy Holidays





-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of bob ellison
Sent: Thursday, January 05, 2012 12:18 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] battery venting; Corrosion



I have had great luck by heating Vaseline to the hot liquid state then brush it on all the exposed lead and I dip the cable ends also.

Doing this I have had 1 terminal that got corroded out of several hundreds.



That gets you a thin coat and lasts for years.

"Clean and tight" is nice but it gets corroded at some point, and I hate cleaning 1 terminal or 20!



Later,

Bob Ellison





-----Original Message-----

From: re-wrenches-bounces at lists.re-wrenches.org

[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems

Sent: Thursday, January 05, 2012 10:37 AM

To: RE-wrenches

Subject: Re: [RE-wrenches] battery venting; Corrosion



Almost all RV's have a small, poorly vented battery box with 4 GC2 batteries. We see corrosion all the time. When we replace batteries, we use zinc coated copper terminals and apply a thin layer of grease with a toothbrush to every exposed portion of the connectors. This simple step, with the occasional reapplication, keeps all terminals as fresh as the day installed for many years. I am speaking from experience of hundreds of installations.



Larry Crutcher

Starlight Solar Power Systems





_______________________________________________

List sponsored by Home Power magazine



List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>






This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120106/eb9ddc4e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.emz
Type: application/octet-stream
Size: 49262 bytes
Desc: image001.emz
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120106/eb9ddc4e/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4427 bytes
Desc: image002.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120106/eb9ddc4e/attachment.png>


More information about the RE-wrenches mailing list