[RE-wrenches] cable spacing in trenches
Ray Walters
ray at solarray.com
Sun Nov 6 11:48:00 PST 2011
Drake;
I had trouble finding that reference, then I found it in the back in
Annex B. I think that would apply to the ampacity of the DC line, but
then for the 12.47 Kv line, I believe you would need Figure 310.60 which
then references Tables 310.60 C (77) thru Table 310.60 c (86)
Without knowing more details, it looks like Jerry would need 24" spacing
(see details 6,8, or 10).
This seems like an issue that you'd want a PE to double check and sign
off on, as that is a fairly high AC voltage, and there could possibly be
a significant induced AC voltage on the DC line (especially if its a
long shared ditch).
Ray Walters
On 11/6/2011 8:36 AM, Drake wrote:
> Check out Figure Figure B.310.15(B)(2)(1)
>
>
>
> At 07:43 AM 11/4/2011, you wrote:
>> Separation is an issue the NEC does not address clearly .However,
>> please make sure you allow adequate room to repair the conduit if
>> damaged, and 12' seems to be the magic number. I lso had no luck
>> looking in 490.
>>
>> NEC 300.4(C)(2)(e) also seems a bit relevant where it allows for
>> conductors of different voltage ratings in manholes "if the
>> conductors of each system are permanently and effectively separated
>> from the conductors of the other systems...", but again this may be
>> referring to separate trenches with different system voltage ratings
>> entering the same manhole for tapping, allowing access for
>> maintenance or other uses.
>>
>>
>>
>> On Thu, Nov 3, 2011 at 5:42 PM, Jerry Caldwell <solarcowboy at yahoo.com
>> <mailto:solarcowboy at yahoo.com>> wrote:
>>
>> Can anyone direct me to the NEC article that stipulates how many
>> inches of separation must be between cables operating at
>> different voltages?
>>
>> I have a project with PV combiner box home runs at 1,000 volts DC
>> in the same trench with 12.47 kV cables. Table 300.5 shows
>> minimum cover requirements for direct burial cables, but this is
>> the distance beneath grade the cables must be. Is there anywhere
>> in the code that calls for a minimum separation distance between
>> cables at different voltages?
>>
>> Thanks,
>> Jerry Caldwell
>>
>>
>>
>>
>> From: Marco Mangelsdorf <marco at pvthawaii.com
>> <mailto:marco at pvthawaii.com>>
>> To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>>
>> Sent: Thursday, November 3, 2011 2:27 PM
>> Subject: [RE-wrenches] under performing Enphase inverters
>>
>> For the first time, several weeks ago, after 40-50 Enphase
>> installs, we've come across at least two M210s that we putting
>> out consistently lower outputs than their immediate neighbors.
>>
>> We replaced the two mods first, which made no difference. Then,
>> in consultation with Enphase, replaced the M210s. After
>> replacing them, the power output was as it should be.
>>
>> Now I've got another suspect system with several underperforming
>> mods out of (36).
>>
>> Has anyone else had this experience?
>>
>> Thanks,
>> marco
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>>
>>
>> --
>> James B Rudolph
>> NABCEP Certified PV Installer
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
> Drake Chamberlin
> ATHENS ELECTRIC LLC
> OH License 44810
> CO license 3773
> NABCEP Certified PV
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111106/c46535b8/attachment-0004.html>
More information about the RE-wrenches
mailing list