At 03:09 PM 10/2/2011, you wrote:
>Sounds like a good situation for a sunny island system.
I second that option. Run high voltage strings (say 13- 30 volt
module strings) to the Sunny Boys, and AC couple to the Sunny
Islands. I'm running 440 feet to a Sunny Boy, and wire size will
not be a problem. You will likely need 4 of the Sunny Islands if you
want to be able to use the entire 15kW array for backup. It is an
expensive option, but if it is a super high end job, then this would
be the way to go.
>Sent from my iPhone.
>
>On Oct 2, 2011, at 12:15 PM, Eric Thomas
><<mailto:solarepiphany at gmail.com>solarepiphany at gmail.com> wrote:
>
>>Wrenches,
>>
>>We are designing a super high end grid-tied w/ battery backup
>>system for a customer. Array will be ~15kW; pole or stand alone
>>structure mounted; 250' from home/batteries. My question is: does
>>it make any sense to invert the power at the array and use this ac
>>to make the long run to the batteries THEN connect to a typical
>>battery charger rather than a dc charge controller? Im mostly
>>concerned with huge dc conductors making this run across the
>>property. Havent delved into the specific design enough to size
>>said conductors yet, or specify any equipment, but wanted to know
>>if im barking up the wrong tree ir not.
>>Thanks for the insight.
>>
>>Eric Thomas
>>Founder
>>Solar Epiphany LLC
>>NABCEP Certified PV Installer
>>WA Electrical Contractor # SOLAREL911NR
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111003/d264a610/attachment-0004.html>
More information about the RE-wrenches
mailing list