Hello Wrenches,
There are certain generators which the XW series inverters find very
difficult to qualify. This is due to the fact that generator coils are
wound in different ways, and even though you may have the voltage and
frequency within specs, there are additional high frequency harmonics on
the generator output that will cause the XW inverter not to accept it.
The critical area of the generator waveform is "zero cross" if there is
ringing at zero cross the generator waveform frequency looks like a
multiple of 60 Hz. The scenario would be rejected by most inverters and it
is correctable using a 15uF 360 VAC oil filled motor run capacitor.
This distortion is greatest for an unloaded generator. Typically the wave
smooths out under load. As mentioned here before you could add a load to
the generator to prove this point, or check the waveform with an
oscilloscope. I know this is not a permanent solution, but it is a good
troubleshooting step.
I don’t disagree with my tech support colleagues about updating the
firmware to V1.07, the changes made on this rev. makes the XW more
tolerant to generators waveform.
To get the latest firmware rev. you can go to our website or email me
directly.
Thank you for the opportunity to participate on the wrenches list,
_____________________________________________________________________________________
Sandra Herrera | Schneider Electric | Renewable Energies Business |
UNITED STATES | Sales Application Engineer
Phone: +425-263-0211 |
Email: sandra.herrera at schneider-electric.com | Site:
www.schneider-electric.com | Address: 161-G South Vasco RD, Livermore,
CA 94551 USA
*** Please consider the environment before printing this e-mail
From:
jay peltz <jay at asis.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
09/09/2011 09:59 AM
Subject:
Re: [RE-wrenches] Help me understand Gen vs XW
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Agreed but it will help with diagnostics.
jay
peltz power
On Sep 9, 2011, at 9:08 AM, William Miller wrote:
Jay:
I disconnected the AGS and the problem persisted. Adding a load may help
but I did not test this. This would require a permanent load and might
not be desirable.
William
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110909/f9821900/attachment-0004.html>
More information about the RE-wrenches
mailing list