William, that was with the stacking cable in place. As you noted, without
the stacking cable the neutral needs to be sized for double the ampacity due
to lack of synchronization. However if the feeder is sized for a 35kW genset
that might not be an issue.

This was on an SW, not a PS, but I'm pretty sure you'll see the same
performance. The two had a lot of similarities at the core.

Phil Undercuffler