On 7/19/2011 2:34 PM, David Brearley wrote:
> Presumably the latter---added as part of the cycle of revisions 
> initiated in 1987.


The array shorting requirement must have gone away near 1993 or 1994 as
I designed an opening and  shorting of the array style GFPD version in
1994 while at Trace Engineering.

It  would have been expensive.

boB







>
>
> On 7/19/11 3:29 PM, "Hans Frederickson" <hans at fredelectric.com> wrote:
>
>     David,
>     Thanks for the interesting history on GFPDs. My copy of the 1987
>     NEC does not have 690-5, and it's not missing any pages. Either my
>     code book is an incomplete printing or perhaps John Wiles was
>     referring to a 1987 proposal that didn't make it into the code
>     until the 1990 NEC.
>
>     Regards,
>     -Hans
>
>     ------------------------------------------------------------------------
>     *From:* re-wrenches-bounces at lists.re-wrenches.org
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>     *David Brearley
>     *Sent:* Tuesday, July 19, 2011 12:57 PM
>     *To:* RE-wrenches
>     *Subject:* Re: [RE-wrenches] 1987 NEC
>
>     Hans,
>
>     John Wiles described the evolution of this standard for a Home
>     Power article that we referenced later in a SolarPro on PV System
>     Ground Faults:
>
>     http://solarprofessional.com/article/?file=SP2_5_pg60_Mync
>
>     "As described by John Wiles, program manager for the Institute for
>     the Energy and the Environment, in the February/ March 2008 Home
>     Power article "Ground-Fault Protection Is Expanding," Article
>     690.5 was added to the /NEC/ in 1987. One of Wiles' first projects
>     in the PV industry was to develop "prototype hardware" to meet the
>     new /Code/ requirement. "The basic concept (of the original GFPD
>     prototype)," writes Wiles, "was to insert a 0.5- or 1-amp circuit
>     breaker in the dc system-bonding conductor." This small circuit
>     breaker senses any current between the grounded current-carrying
>     conductor and the grounding system, tripping if current exceeds
>     the 0.5 A or 1 A rating. By mechanically linking this smaller
>     breaker to larger capacity breakers that are installed inline with
>     the ungrounded current-carrying array conductors, it is possible
>     to detect, interrupt and indicate that a ground fault has
>     occurred, and to disconnect the fault.
>
>     These early GFPDs were manufactured for 48 V or lower PV systems.
>     According to Wiles, "As higher voltage, utility-interactive PV
>     inverters became available in the late 1990s, using a 0.5- or
>     1-amp fuse as the sensing element and the inverter's control
>     electronics to monitor the fuse was more cost effective." While
>     the sensing equipment may have changed, in general the role of the
>     modern GFPD remains the same as it was in 1987:
>
>     1. Detect ground faults in PV arrays.
>     2. Interrupt the fault current.
>     3. Indicate that a ground fault has occurred.
>     4. Disconnect the faulted part of the array.
>
>     These four GFPD requirements for grounded PV arrays are spelled
>     out in /NEC/ 690.5(A) and 690.5(B). The former requires
>     ground-fault detection and interruption (GFDI), which includes the
>     provision to indicate the presence of a ground fault. The latter
>     requires that faulted circuits be isolated either by disconnecting
>     the ungrounded conductors of the faulted circuit or by shutting
>     down power to the output power circuits of the inverter or charge
>     controller.
>
>     A final GFPD requirement is found in Article 960.5(C), which calls
>     for a visible warning in the proximity of the ground-fault
>     indicator. The warning could be an LED, an LCD or both. In
>     general, the manufacturer provides this electric shock hazard
>     warning as part of the listed grid-tied inverter or charge
>     controller. However, where a PV system includes batteries, the
>     installer must apply a duplicate warning label near the batteries,
>     stating:
>
>     WARNING
>     ELECTRIC SHOCK HAZARD
>     IF A GROUND FAULT IS INDICATED, NORMALLY
>     GROUNDED CONDUCTORS MAY BE UNGROUNDED
>     AND ENERGIZED
>
>
>     One change in the GFPD requirements introduced in 1987 is that it
>     is no longer necessary to short-circuit, or "crowbar," the PV
>     array in the event of a ground fault. This added step had the
>     effect of reducing the PV array voltage to zero, minimizing shock
>     hazard. The requirement was dropped in a subsequent /Code/ cycle,
>     as leaving the array in a short-circuited condition created
>     several other issues."
>
>
>     If you're a Home Power subscriber, you can access the original
>     article in the HP archives. If not, it is summarized above.
>
>     Best,
>
>     David Brearley, Senior Technical Editor
>     /SolarPro/ magazine
>     NABCEP Certified PV Installer ^(TM)
>     david.brearley at solarprofessional.com
>     Direct: 541.261.6545
>
>
>     On 7/19/11 2:19 PM, "Hans Frederickson" <hans at fredelectric.com> wrote:
>
>         Kent,
>         I'm not a geezer yet, but thanks to my dad I do have a  copy
>         of the 1987 NEC. 690-5 (Ground Fault Detection and
>         Interruption) was  added in the 1990 NEC. There is no 690-5 or
>         mention of ground fault  detection/interruption in the 1987 NEC.
>
>         In the 1990 NEC, section 690-5 is very small compared to 690.5
>         in  the 2011 NEC. Here's the complete text from 1990:
>
>         "690-5. Ground Fault Detection and Interruption.  Roof-mounted
>          photovoltaic arrays located on dwellings shall be provided
>         with ground-fault  protection to reduce fire hazard. The
>         ground-fault protection circuit shall be  capable of detecting
>         a ground fault, interrupting the fault path, and  disabling
>         the array."
>
>         The handbook for 1990 goes on to say that the gfp device  must:
>         1) detect the ground fault
>         2) open the grounded conductor to  interrupt the ground fault
>         3) open the ungrounded conductors and short the  photoltaic
>         array source to disable it
>
>         For some reason, I've never heard of item #3, specifically the
>         part  about shorting the array. Can anyone shed light on  this?
>
>         Regards,
>         -Hans
>
>
>         ------------------------------------------------------------------------
>         *From:* re-wrenches-bounces at lists.re-wrenches.org
>          [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf
>         Of *Kent Osterberg
>         *Sent:* Monday, July 18, 2011 10:07  PM
>         *To:* gary at icarussolarservices.com;  RE-wrenches
>         *Subject:* Re: [RE-wrenches] 1987 NEC
>
>         Gary,
>
>         No one else has  come up with a 1987 NEC. If you can get a
>         copy of 1987 section 690.5 (I think  it was 690-5 back then),
>         I'd appreciate it.
>
>         Kent Osterberg
>         Blue  Mountain Solar
>
>
>
>         Gary Willett wrote:
>
>             Kent:
>
>             I am a member of the  International  Association of
>             Electrical Inspectors (IAEI), and they're  headquartered
>             here in  the Dallas area.
>
>             If you aren't successful  getting the info from a  Wrench
>             with the 1987 code book, let me know  and I am sure I can
>             request a  FAXed copy of 1987 section  690.5.
>
>
>
>
>
>             Regards,
>
>             Gary Willett, PE
>             Gary at IcarusSolarServices.com
>
>             On  7/15/2011 4:30 PM, Kent Osterberg  wrote:
>
>                 I'm looking  for the text of 1987 NEC 690.5  to
>                 compare with 2011 version. If any of you  geezers have
>                 kept copies  that old, please contact me off list.
>                 Thanks.
>
>                 Kent Osterberg
>                 Blue Mountain Solar
>                 _______________________________________________
>
>
>
>
>     ------------------------------------------------------------------------
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110719/6e1c96d6/attachment-0004.html>


More information about the RE-wrenches mailing list