[RE-wrenches] 24 volt Battery Bank comparison
James Jefferson Jarvis
jj at aprsworld.com
Tue May 31 18:19:59 PDT 2011
On 2011-05-31 20:14, Tom Elliot wrote:
> Good on the buss bars Wayne. Using them removes the concerns about
> multiple strings and increases redundancy and system stability. You
> won’t need 4/0 between single strings and the buss bar, you can probably
> easily use smaller cable, just size it for the individual string. 4/0 to
Part of the argument for having multiple strings is for redundancy. If
smaller interconnect cables are used, they will likely not have the
required ampacity and OCPD to support the full load. In the event of
part of the bank needing to be pulled offline there will be downtime and
expense associated with upgrading the smaller interconnect cables to
support the full load or the proportionally increased load.
Food for thought,
-James Jarvis