[RE-wrenches] 24 volt Battery Bank comparison

Jason Szumlanski Jason at fafcosolar.com
Tue May 31 17:21:44 PDT 2011


Just another thought- If redundancy is an issue with string sizing, having a 12v inverter handy is sometimes a viable backup option with a 24v bank with 2 or more parallel strings. 

Jason Szumlanski
Fafco Solar

On May 31, 2011, at 7:55 PM, "Jason Szumlanski" <Jason at fafcosolar.com> wrote:

> If the choice is one or three, I choose one. If the choice is one or two, I choose two for the same redundancy benefit echoed by others. However, it sometimes depends how remote the system is. 
> 
> If you are a few miles down the road from a stocking battery distributor, one string is great. If you are a boat ride or a 10 hour 4x4 crawl at 2 mph away, redundancy may be critical. It all depends on the situation. I would even consider three strings if the location has serious access problems and the customer can only "survive" with 33% capacity loss for a period of time.
> 
> While I have my favorite brands, sometimes you have to go with a brand that fits the right capacity and string arrangement. Fortunately Rolls has lots of options, so you should find a suitable alternative. I start with my desired V, aH, and parallel strings, then let the manufacturer or distributor do the work and recommend options. Not that I don't do my research, but sometimes they come up with a better option than you initially think of.  
> 
> Jason Szumlanski
> Fafco Solar
> 
> On May 31, 2011, at 6:25 PM, "Brian Mehalic" <brian at solarenergy.org> wrote:
> 
>> Hi Wayne-
>> While I think a lot of folks will agree that a single string is better for the long term health of the batteries as it results in more even charging, I still like the idea of at least two strings.  That way if a single battery fails, that string can be removed and the end-user can at least get by on half of the pack until a replacement can be installed.
>> Brian
>> 
>> On Tue, May 31, 2011 at 10:19 PM, James Surrette <james at surrette.com> wrote:
>> Hi Wayne,
>> 
>> I look forward to the input from the wrenches.
>> 
>> My recommendation, regardless of the brand, would be for one string.
>> 
>> Regards,
>> 
>> Jamie
>> 
>> >>> Wayne Irwin <wayne at pureenergysolar.com> 5/31/2011 6:49 PM >>>
>> Hello Esteemed Battery Gurus,
>> 
>> Which of the following do you believe is the better 24 V battery bank?
>> 
>> A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)
>> 
>> or
>> 
>> B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)
>> 
>> Thank you in advance for your input!
>> 
>> 
>> Wayne Irwin, EE
>> Director of Engineering
>> Pure Energy Solar International Inc. 
>> State Licensed Solar Contractor
>> License # CVC56695 
>> Wayne at PureEnergySolar.com
>> http://pureenergysolar.com
>> 352 377-6527 Office
>> 352 336-3299 Fax
>> 352 316-1637 Cell
>> The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your computer system. Thank you.
>> 
>> 
>> This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content. The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> 
>> -- 
>> ========================
>> Brian Mehalic 
>> NABCEP Certified Solar PV Installer™ R031508-59
>> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>> PV Curriculum Developer and Instructor
>> Solar Energy International
>> Carbondale, CO 81623
>> http://www.solarenergy.org
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110531/7fb8d93a/attachment-0004.html>


More information about the RE-wrenches mailing list