[RE-wrenches] SMA High AC Voltage vs MPP
Drake
drake.chamberlin at redwoodalliance.org
Thu May 12 16:33:44 PDT 2011
Jamie,
Thanks for the reply. That does make sense as to how the AC Voltage
might affect an inverter. It would certainly seem a likely issue
with the Sunny Boy line of inverters up to the 7000, which have a
maximum MPP DC Voltage of 250 V. The SB 8000 is a 300 V MPP unit. I
wonder if the Sunny Design tool is correct about the concern. I also
wonder why the SB 8000 went to 300 V DC.
Drake
At 01:17 PM 5/12/2011, you wrote:
>Drake,
>
>The sunny boy design tool assumes a max grid voltage of 240 (I have
>version 1.56 that allows you to select 250vAC as the max on screen
>#2), if your grid voltage exceeds the grid design voltage then the
>minimum mpp design voltage needs to increase along with it in order
>to maximize your kWh production.
>
>I forget what the difference is between grid and minimum mpp, IIRC
>it is 10vDC+ above Grid Voltage so 240vAC would require 250vDC as
>the minimum mpp. You would need to check the installation manual
>for the sunny boy inverter that you are installing.
>
>At high temps, the mpp voltage drops (calculate this as %/deg c
>above 25 deg c from your module manufacturer supplied temp coef) and
>may drop below the minimum designed mpp needed for 240vAC or
>250vAC. If this happens then either the mppt will adjust below the
>knee of the power curve in order to increase the voltage (less
>efficient), or the mpp voltage will drop below the minimum needed
>and the inverter may shut off. I have seen both happen.
>
>
>
>Jamie Johnson
>NABCEP Certified PV Technical Sales Professional
>NABCEP Certified Solar PV Installer
>
>General Manager
>SOLAR POWER ELECTRIC
>[]
>
>
>
>-------- Original Message --------
>Subject: [RE-wrenches] SMA High AC Voltage vs MPP
>From: Drake
><<http://drake.chamberlin@redwoodalliance.org>>drake.chamberlin at redwoodalliance.org>
>Date: Thu, May 12, 2011 12:27 pm
>To: RE-wrenches
><<mailto:re-wrenches at lists.re-wrenches.org>re-wrenches at lists.re-wrenches.org>
>
>Hello Wrenches,
>
>Using the Sunny Design tool, I got a message saying the design was
>conditionally compatible. The message said:
>
>"In case of increased grid voltage, the operating point of the PV
>generator may slightly deviate from its MPP if the module
>temperature is high. This design can therefore only be recommended
>if the expected average grid voltage at the inverter will not exceed
>the value used in the calculation."
>
>The SMA tech rep I talked to thought the design was good, but
>couldn't really answer the questions I had. These are:
>What is the design AC voltage?
> * Is it 240 VAC or the maximum voltage the inverter allows,
> which is 264 VAC?
> * There is no input for design AC voltage.
> * Why does the max AC voltage affect the MPP at high temperature?
> * Since it apparently does, how much does it affect it?
> * If the grid voltage got to 250 VAC, would that be a problem?
> * I see that range pretty regularly around here.
>Any help with these questions would be appreciated.
>
>Thank you,
>
>Drake
>
>Drake Chamberlin
>ATHENS ELECTRIC
>OH License 44810
>CO license 3773
>NABCEP Certified PV
>
>----------
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>Content-ID: <sigimg1 at 62c9f17e3d1ba368dd28bc0b725c6948>
>Content-Type: image/jpeg;
> name="sigimg1";
>Content-Disposition: inline;
> filename="sigimg1";
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
ATHENS ELECTRIC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110512/ac772d10/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 265e27e.jpg
Type: image/jpeg
Size: 41494 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110512/ac772d10/attachment-0007.jpg>
More information about the RE-wrenches
mailing list