[RE-wrenches] PVC running through the house
Nick Soleil
nicksoleilsolar at yahoo.com
Sat Apr 9 10:35:43 PDT 2011
As per the 2011 NEC, MC (metal clad cable) is now allowed to be run inside the
building envelope for solar output circuits.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
________________________________
From: Peter Parrish <peter.parrish at calsolareng.com>
To: Keith Cronin <electrichi01 at yahoo.com>; RE-wrenches
<re-wrenches at lists.re-wrenches.org>
Sent: Thu, April 7, 2011 4:23:52 PM
Subject: Re: [RE-wrenches] PVC running through the house
The Code back then was a little vague back then and I am not sure it has
been improved.
First, there needs to be a DC disconnect just before or just after
penetrating the building shell. Most AHJ allowed us to place this disconnect
in the attic within reach of the access door. Once we needed to place the DC
disconnect on the roof and we were able to get away with a fused combiner
box. Another time we actually needed to put a 600V 3-pole fused disco on the
roof.
Second, and this is really an obscure point. Only conduit, raceways and the
like (not cable runs) were allowed in the attic space and walls. So FMC is
okay but MC is not. It is an issue of unfortunate terminology.
Third, you need to label the conduit “Caution – Solar Circuit”, even in the
walls.
Finally, where the conduit passes thru studs, you need protection plates on
the studs to prevent screws or nails piercing the conduit.
That’s my story and I’m sticking to it.
-Peter
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
________________________________________
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Keith Cronin
Sent: Thursday, April 07, 2011 3:05 PM
To: RE-Wrenches
Subject: [RE-wrenches] PVC running through the house
Hi folks
Was wondering- does anyone know back in 2005, if it was permissible to run
DC conductors from the roof, through the home to the inverter location,
inside the house, per the NEC?
Thanks
Keith Cronin
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110409/f670a307/attachment-0004.html>
More information about the RE-wrenches
mailing list