[RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs
Exeltech
exeltech at yahoo.com
Wed Mar 30 16:00:41 PDT 2011
You're overlooking an important fact.
Grid-tie inverters are current-limited devices. They lack surge capability.
Trip times for various circuit breakers vary depending in part on the overload as a percentage of the breaker's ratings and the circuit breaker temperature (for thermal breakers).
A properly operating UL1741-certified grid-tie inverter that's exposed to a sudden dead short in the AC output will stop producing current before the circuit breaker would trip.
Dan
--- On Wed, 3/30/11, Mark Frye <markf at berkeleysolar.com> wrote:
From: Mark Frye <markf at berkeleysolar.com>
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date: Wednesday, March 30, 2011, 3:38 PM
Right, so going totally on the fly at the white board, let's
say we have an inverter with a 45A AC output, it see's the short and pours it's
little heart out at 45A for 0.1 sec before shutting out, delivering 4.5 A-sec of
energy into the fault. Meanwhile we take out a clearing time curve
for the generic 60A breaker that the inverter would be backfeed at the
other end of the feeder. It will deliver 10 times it's rating or 600A for 0.5
secs before clearing. That's 300 A-sec of energy, 66 times more than the
inverter.
So can we say that when looking at sizing the AC side of these
inverters we need more to concern ourselves with continuous overload
conditions and not so much with short-circuit/ground fault
conditions?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA
95959
(530)
401-8024
www.berkeleysolar.com
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Exeltech
Sent: Wednesday, March 30, 2011 12:04 PM
To:
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used
tocombinemultipleinverter outputs
Per your question:
> 1 - What does a UL1741 inverter do when it is
connected
> to a line that is experiencing a short-circuit or ground
fault?
Presuming a hard short, the voltage in that
circuit would be essentially zero, and a UL1741 compliant inverter would
cease producing power in less than 0.1 second.
Dan
Sr.
Engineer
Exeltech
--- On Wed,
3/30/11, Mark Frye <markf at berkeleysolar.com> wrote:
From:
Mark Frye <markf at berkeleysolar.com>
Subject: Re: [RE-wrenches]
sizing a sub-panel used tocombine multipleinverter outputs
To:
"'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date:
Wednesday, March 30, 2011, 12:37 PM
#yiv1838450963 UNKNOWN {
FONT-FAMILY:Helvetica;}
#yiv1838450963 UNKNOWN {
FONT-FAMILY:Helvetica;}
#yiv1838450963 UNKNOWN {
FONT-FAMILY:Calibri;}
#yiv1838450963 UNKNOWN {
FONT-FAMILY:Tahoma;}
#yiv1838450963 UNKNOWN {
}
That is a really good question Brian.
Mostly when thinking about these sizing issues I think about
overload conditions and not so much about short-circuit and ground fault
conditions.
So two questions come up:
1 - What does a UL1741 inverter do when it is connected to a
line that is experiencing a short-circuit or ground
fault?
2 - What does the feeder breaker do when it is connected to a
line that is experiencing a short-circuit or ground
fault?
As far as number two, thanks to all the great work we do
establishing low impedence fault paths back to circuirt protectors, the
breaker is going to trip at it's rating and protect the wire at the same
rating. But that doesn't mean that the conductor won't see more
than rated amps during the fault. It will see alot more than
for a very short time. During this very short time frame, the actual
currents flowing into the fault from the utility side of the equation
far far exceed the currents contributed by the power limited inverter
side.
Mark
Frye
Berkeley
Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Brian Teitelbaum
Sent: Wednesday, March 30, 2011 10:02
AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing
a sub-panel used tocombine multipleinverter outputs
Wouldn’t
a fault in that conductor between the main and the sub have a potential
for up to 160A of current? I would think that at noon on a sunny day,
the inverter system could produce 80A from one direction (albeit really
only the max amperage outputs of the inverters) and 80A of grid current
from the main into a partial fault.
Brian
Teitelbaum
AEE
Solar
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Mark Frye
Sent: Wednesday, March 30, 2011 9:49
AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches]
sizing a sub-panel used to combine multipleinverter
outputs
Al,
I would
say that yes the meter is a load and this goes to show the relative
inadequacy of the vocabulary we are using in the discussion. In the
example we have been using with the 80A breaker, wire and sub panel, you
could have up to 80A of loads installed in the sub and still not create
an over current condition in any of that equipment.
Mark
Frye
Berkeley
Solar Electric Systems
303
Redbud Way
Nevada
City, CA 95959
(530)
401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Al Frishman
Sent: Wednesday, March 30, 2011 9:00
AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches]
sizing a sub-panel used to combine multipleinverter outputs
Is
a monitoring system installed in the Load Center to measure the
cumulative kWh’s of the inverter’s considered a load?
The
type of monitoring device I am talking about has CT’s that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar. The digital
Meter has a 3-pole 5A breaker in it so the conductors in the load center
can be connected to lugs on the bus bar directly.
Al
Frishman
AeonSolar
(917) 699-6641 -
cell
(888)
460-2867
www.aeonsolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Jason Szumlanski
Sent: Wednesday, March 30, 2011 8:18
AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing
a sub-panel used to combinemultipleinverter
outputs
Another
key is to remember that this discussion also applies to the conductor
between the main panel and subpanel. In a large PV system, this could
result in a pretty large wire between the two panels, and a significant
cost that is often overlooked. In some cases it makes sense to locate
the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.
And
because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example)
in the subpanel doesn’t change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can’t size
the wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A.
(not that it makes much of a difference in this example, but it still
must be considered)
At
least that’s how I understand it…
Jason
Szumlanski
Fafco
Solar
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Mark Frye
Sent: Wednesday, March 30, 2011 1:33
AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches]
sizing a sub-panel used to combinemultipleinverter
outputs
Opps!
My bad,
I was thinking of a single phase system, not the three phase
system shown in the article.
For the
three phase system Kent is correct in counting 180A of supply per
bar.
Mark Frye
Berkeley
Solar Electric Systems
303 Redbud Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Mark Frye
Sent: Tuesday, March 29, 2011 10:17
PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches]
sizing a sub-panel used to combine multipleinverter outputs
I think
Kent and I agree. For the case where the subpanel is not dedicated
a PV sub-panel he is calculating for 2 - 50A breakers and I calculated
for 3 - 50A breakers.
Mark Frye
Berkeley
Solar Electric Systems
303 Redbud Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Kent Osterberg
Sent: Tuesday, March 29, 2011 9:26
PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing
a sub-panel used to combine multiple inverter outputs
Per
705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is
required and the inverters would have to feed the opposite end of the
bus bars. If no, the code is not clear on the requirement, but obviously
the 80-amp breaker in the main panel limits the maximum current flowing
through the sub-panel.
Kent Osterberg
Blue Mountain
Solar
-----Inline Attachment Follows-----
_______________________________________________
List
sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options
& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List
rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check
out participant
bios:
www.members.re-wrenches.org
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110330/350de9d8/attachment-0004.html>
More information about the RE-wrenches
mailing list