[RE-wrenches] 690.14 (4) Max Number of Disconnects
Darryl Thayer
daryl_solar at yahoo.com
Wed Jan 12 13:49:31 PST 2011
I had a similar situation in Minnesota, my local inspector was puzzeled but the
regional inspector said ABSOLUTLY the solar equipment has to be shut off with
no more than 6 motions of the hand. I combined the AC into a panel of 12
breakers, with one main (i had 12 inverters). For the DC side I did something
DT but I could have used 2 each 6 pole Square D 600 volt 30 amp Disconnects
or 3 each 4 pole, or 4 each 3 pole to complete the disconnect requirement
Darryl
________________________________
From: Al Frishman <amfrish at aeonsolar.com>
To: re-wrenches at lists.re-wrenches.org
Sent: Wed, January 12, 2011 3:11:17 PM
Subject: [RE-wrenches] 690.14 (4) Max Number of Disconnects
Hi Wrencher’s
I am working on a system with 10 inverters. The output of all 10 single phase
inverters will be combined in a main lug only panel located on the 8th floor
(each inverter will have a 2 pole breaker). The MLO Panel will be protected by
a fused switch located in the basement. Does the panel on the 8th floor used to
combine all 10 inverters need to have a main breaker in order to comply with
690.14 (4)?
Any and all feedback is appreciated.
Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com