[RE-wrenches] XW on 120v
Sandra.Herrera at schneider-electric.com
Sandra.Herrera at schneider-electric.com
Thu Oct 27 13:05:20 PDT 2011
Hello Jay,
If the XW is already configured as a single phase 120V, then it will
connect to a 120V generator. But if the XW is configured as 120/240V, then
a single phase 120V generator will not work.
_____________________________________________________________________________________
Sandra Herrera | Schneider Electric | Renewable Energies Business |
UNITED STATES | Sales Application Engineer
Phone: +425-263-0211 |
Email: sandra.herrera at schneider-electric.com | Site:
www.schneider-electric.com | Address: 161-G South Vasco RD, Livermore,
CA 94551 USA
*** Please consider the environment before printing this e-mail
From:
jay peltz <jay at asis.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
10/27/2011 11:35 AM
Subject:
[RE-wrenches] XW on 120v
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Hi All,
I seem to remember that you can connect the XW inverters with 120v and
they will battery charge.
Anybody know for sure?
thanks,
jay
Peltz power
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111027/ca8682ec/attachment-0003.html>
More information about the RE-wrenches
mailing list