[RE-wrenches] Push-in Wire Connectors
Glenn Burt
glenn.burt at glbcc.com
Thu Oct 20 13:55:38 PDT 2011
Kent,
Can you direct me to a code citation that says that splices made inside a
NEMA 4 rated enclosure must be suitable for the location of the enclosure,
and not the protection level afforded by the enclosure?
I have had this discussion and lean toward the other side that splices made
in the enclosure need only be rated to the protection rating of the
enclosure, as long as all conduits are properly terminated with fittings
that meet the minimum rating of the enclosure.
Thanks,
Glenn Burt
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Thursday, October 20, 2011 12:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Push-in Wire Connectors
Jason,
The roof is a wet location so connectors rated for wet locations are
required. The NEMA 4 rating of the junction box doesn't change matters.
Kent Osteberg
Blue Mountain Solar
Jason Szumlanski wrote:
Anyone see a problem using Ideal In-Sure Push-In Wire Connectors in a NEMA 4
roof mounted PVC junction box? Specifically, Ideal Model 39 for splicing #10
AWG.
They are 105C, 600V rated, but not rated for wet locations. I've had
inspectors require wet location rated twist-on wire connectors before in
these boxes. I foresee an issue.
Unfortunately, these connectors were not addressed in John Wiles code corner
Making Connections article in 2003. May be time for an update!
Jason Szumlanski
Fafco Solar
_____
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111020/b61f6b8c/attachment-0003.html>
More information about the RE-wrenches
mailing list