[RE-wrenches] 24 volt Battery Bank comparison

boB Gudgel boB at midnitesolar.com
Thu Jun 2 09:32:26 PDT 2011


On 6/2/2011 9:03 AM, Darryl Thayer wrote:
> Excellent comment tom, so true.  I get concerned that some of my 
> experiences are a collection of exceptions.  I like Larry's comments 
> because he has worked so many systems.  I have seen fires, but  mostly 
> because I have a reputation and people wnat me to come and see what 
> happened.
> Darryl
>

Now my question would be...  Why ?

I have to think that with more batteries in the system, they are just 
not getting charged as well.

If that's the case, I think this could be fixed. Haven't battery 
chargers and education gotten
better since 1967, Tom ?

boB


> ------------------------------------------------------------------------
> *From:* The Solar Powered Office of Tom Duffy <tom at thesolar.biz>
> *To:* Allan at positiveenergysolar.com; 'RE-wrenches' 
> <re-wrenches at lists.re-wrenches.org>
> *Sent:* Thursday, June 2, 2011 9:34 AM
> *Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
>
> Wrenches:
> This is a really great thread. Here’s my two cents…
> I started selling and configuring battery systems when I got out of 
> the Army back in 1967 I’m a marine electrician. In the boat 
> environment everybody tries to make a big battery out of a bunch of 
> small batteries, Over the years this is what I’ve witnessed; All else 
> being equal.
> 3 parallel strings = 4 ½  to 5 ½ years Max
> 2 parallel strings = 5 ½ to 6 ½ years Max
> 1 series string = 8 to 12 years Max
> The above seems to hold true if the charge settings, Bulk, Absorb time 
> and Voltage are correctly set. But as we all know 85% of the time this 
> is not the case.
> So my conclusion is that parallel configured banks just about cut the 
> life in half.
> And there is always the stories about the guy that drank a quart of 
> Bourbon a day and smoked cigars chasing women until he was 102 years 
> old. The same is true with batteries… the exception but not the rule.
> ***Tom Duffy*
> /  Systems Design Engineer///
> tom at thesolar.biz <mailto:tom at thesolar.biz>
> 575-539-2111 X 122
> //Although no trees were killed in the sending of this message, a 
> large number of electrons were terribly inconvenienced.//
> **Confidentiality Notice**:This message including any attachments is 
> for the sole use of the intended recipient(s) and may contain 
> confidential and privileged information. Any unauthorized review, use, 
> disclosure or distribution is prohibited. If you are not the intended 
> recipient, please contact the sender and delete any copies of this 
> message.
> ------------------------------------------------------------------------
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of 
> *Allan Sindelar
> *Sent:* Wednesday, June 01, 2011 11:07 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
> I had done this a few times in the distant past, and also had done it 
> in recent years on my own previous battery bank (four strings of 
> S-530s - yes, I know; it was in anticipation of future plans to 
> upgrade to 48V, and two strings wouldn't have been enough).
>
> It worked fine - and that turned out to be a problem. I had noticed 
> reduced capacity, but assumed foolishly that it was simply to age and 
> cycle life (going on six years and three teenagers). Found out I had 
> two failed cells in two different strings. The parallel connections 
> probably - I'm not sure here - allowed the bank to perform more 
> robustly and less obviously weakened. It might have even allowed the 
> bank to perform as if both failed cells had been in the same string. 
> But it also allowed me to not pay enough attention to a potentially 
> serious problem by disguising it.
>
> I blame myself more than the parallel connectors (just some #2 
> interconnects I had lying around). I'm just not sure I would use it on 
> a customer's system.
> *Allan Sindelar*
> Allan at positiveenergysolar.com <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe , New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
>
> On 6/1/2011 9:20 AM, toddcory at finestplanet.com 
> <mailto:toddcory at finestplanet.com> wrote:
> Does it make any difference to do as boB recently suggested and 
> inter-connect the strings? So in other words, if you have two parallel 
> strings, what happens if you parallel each battery in one string with 
> the battery in the other string? Has anyone tried this? It might help 
> insure more balance between each series string.
> Todd
> On Wednesday, June 1, 2011 3:06am, "James Surrette" 
> <james at surrette.com> <mailto:james at surrette.com> said:
> Hi boB,
> I would say maintenance is a large issue - especially when dealing 
> with L-16's or the like, as the number of cells & connections gets 
> large, i.e. 1000-1200AH @ 48VDC is three (3) strings, 24 batteries and 
> 72 cells.  Will a client water 24 cells...maybe - 72??
> However, from Tech Support days, imbalance is the larger problem.  It 
> seems to take 18 months - 3 years and then you would get SG readings 
> where one (1) bank was perfect and the other(s) is significantly 
> lower......which is hard to overcome without effort (either break the 
> banks & charge independently or hammer the banks and allow the high 
> string to get even higher).
> One of the key take aways that often gets overlooked is the proper 
> initial activation of the strings.  It is impossible for all cells to 
> have identical resting voltage.  During commissioning, each string 
> should be charged to 2.45-2.5VPC and held until all cells read the 
> same voltage.  If running multiple strings, then connect the strings 
> and run the entire bank at 2.45-2.5VPC until all cells measure the 
> same voltage.  Now the bank is well balanced and the chances of a 
> major imbalance are greatly reduced.  However, even after this effort, 
> if you use an amp clamp, you will notice slight differences in the 
> amount of current being accepted by each bank.
> Best,
> Jamie
>
>
>
> >>> boB Gudgel <boB at midnitesolar.com> <mailto:boB at midnitesolar.com> 
> 6/1/2011 5:00 AM >>>
> On 5/31/2011 11:25 PM, Tom Elliot wrote:
>
>     Bob,
>     I totally understand the concern about multiple strings *if the
>     strings are connected across the battery bank* as had always been
>     the tradition in off-grid installations.  My own experience with
>     such a bank in my system  showed why when I had a single cell get
>     to near meltdown.  I was lucky to find it.
>
>
>
> This might be a good reason for an installer to have one of those FLIR 
> (or similar) thermal imager cameras.   They're a bit on the expensive 
> side, but could
> really be helpful for so many things.   Even just to know if you have 
> left a nut loose (under load of course)
>
> boB
>
>
>     Maintenance is another reason, such banks are far more difficult
>     to maintain.  But I think those concerns are ameliorated a great
>     deal with a buss bar installation and once I did that I never had
>     another problem and found the battery bank much easier to maintain
>     because the strings no longer had to be right next to each other. 
>     Heck, it would be possible to put each series string in its own
>     box for that matter.  And with the inclusion of string fuses that
>     reduces problems even further.
>     When living with an off-grid system my biggest concern was system
>     reliability and redundancy and the idea of a single string failure
>     was a big worry which is why I never would consider it.
>     Tom
>     **From:**boB Gudgel <mailto:boB at midnitesolar.com>
>     **Sent:**Tuesday, May 31, 2011 8:16 PM
>     **To:**RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
>     **Subject:**Re: [RE-wrenches] 24 volt Battery Bank comparison
>
>
>     OK, I've been hearing for years now that one battery string is
>     best and maybe two but no more should be used.
>
>     What is the reason for this fear ???    What is the experience
>     with multiple strings in parallel ??
>
>     If it is because of current sharing of the strings, that shouldn't
>     be an insurmountable problem if the wiring is done right.
>
>     If it has to do with the possibility of fire, which Darryl
>     mentioned, seems that series string fuses could mitigate the
>     possibility of that issue, if because of shorted cells, just like
>     PV combiners.
>
>     Or maybe it has to do with the trouble of getting into the middle
>     of a pile of batteries ?  Use battery boxes ?
>
>     The strings are in parallel and so they all get the same voltage,
>     theoretically anyway if the connections are good.
>
>     I would think that the more strings, the LESS stress on individual
>     batteries, not more.  The current in each battery should be less
>     than it would be I would think.
>
>     So what is the real experience ??
>
>     Is a battery balancer the answer ??
>
>     Thanks,
>     boB
>
>
>
>
>
>         On May 31, 2011, at 8:23 PM, "Wayne Irwin"
>         <wayne at pureenergysolar.com <mailto:wayne at pureenergysolar.com>>
>         wrote:
>
>             I think the verdict is**12** - Rolls 2-YS-31 2430 AH @ 20
>             HR (one string) and one dry spare in storage is the best
>             case scenario!
>
>             Wayne Irwin, EE
>             Director of Engineering
>             Pure Energy Solar International Inc.
>             State Licensed Solar Contractor
>             License # CVC56695
>             Wayne at PureEnergySolar.com <mailto:Wayne at PureEnergySolar.com>
>             http://pureenergysolar.com
>             352 377-6527 Office
>             352 336-3299 Fax
>             352 316-1637 Cell
>
>     ------------------------------------------------------------------------
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>     ------------------------------------------------------------------------
>     No virus found in this message.
>     Checked by AVG - www.avg.com <http://www.avg.com>
>     Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date:
>     05/31/11
>
>     _______________________________________________
>     List sponsored by Home Power magazine
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
> This email and its attachments have been scanned by iConnection E-Mail 
> Firewall for viruses, spam, and malicious content. The information 
> transmitted in this email is intended only for the entity or person to 
> which it is addressed and may contain confidential/privileged 
> material. If you received this in error, please contact the sender and 
> delete the material from any computer. Any review, retransmission, 
> dissemination, or other use of this information by persons or entities 
> other than the intended recipient is strictly prohibited. %^^%
>     
>
>     
> _______________________________________________
> List sponsored by Home Power magazine
>     
> List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>     
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     
> List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>     
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>     
> Check out participant bios:
> www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>     
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org 
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110602/8f38fc3a/attachment-0003.html>


More information about the RE-wrenches mailing list