Per your question:
> 1 - What does a UL1741 inverter do when it is connected
> to a
line that is experiencing a short-circuit or ground fault?
Presuming a hard short, the voltage in that circuit would be essentially zero, and a UL1741 compliant inverter would cease producing power in less than 0.1 second.
Dan
Sr. Engineer
Exeltech
--- On Wed, 3/30/11, Mark Frye <markf at berkeleysolar.com> wrote:
From: Mark Frye <markf at berkeleysolar.com>
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombine multipleinverter outputs
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date: Wednesday, March 30, 2011, 12:37 PM
_filtered #yiv1283215088 {
font-family:Helvetica;}
_filtered #yiv1283215088 {
font-family:Helvetica;}
_filtered #yiv1283215088 {
font-family:Calibri;}
_filtered #yiv1283215088 {
font-family:Tahoma;}
_filtered #yiv1283215088 {
}
That is a really good question Brian.
Mostly when thinking about these sizing issues I think about
overload conditions and not so much about short-circuit and ground fault
conditions.
So two questions come up:
1 - What does a UL1741 inverter do when it is connected to a
line that is experiencing a short-circuit or ground fault?
2 - What does the feeder breaker do when it is connected to a
line that is experiencing a short-circuit or ground fault?
As far as number two, thanks to all the great work we do
establishing low impedence fault paths back to circuirt protectors, the breaker
is going to trip at it's rating and protect the wire at the same
rating. But that doesn't mean that the conductor won't see more
than rated amps during the fault. It will see alot more than for a
very short time. During this very short time frame, the actual currents flowing
into the fault from the utility side of the equation far far exceed the currents
contributed by the power limited inverter side.
Mark Frye
Berkeley Solar Electric
Systems
303 Redbud
Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Brian
Teitelbaum
Sent: Wednesday, March 30, 2011 10:02 AM
To:
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used
tocombine multipleinverter outputs
Wouldn’t
a fault in that conductor between the main and the sub have a potential for up
to 160A of current? I would think that at noon on a sunny day, the inverter
system could produce 80A from one direction (albeit really only the max amperage
outputs of the inverters) and 80A of grid current from the main into a partial
fault.
Brian
Teitelbaum
AEE
Solar
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To:
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combine multipleinverter outputs
Al,
I would
say that yes the meter is a load and this goes to show the relative inadequacy
of the vocabulary we are using in the discussion. In the example we have been
using with the 80A breaker, wire and sub panel, you could have up to 80A of
loads installed in the sub and still not create an over current condition in any
of that equipment.
Mark
Frye
Berkeley
Solar Electric Systems
303
Redbud Way
Nevada
City, CA 95959
(530)
401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Al
Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To:
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combine multipleinverter outputs
Is
a monitoring system installed in the Load Center to measure the cumulative kWh’s
of the inverter’s considered a load?
The
type of monitoring device I am talking about has CT’s that go around the
conductors and the Voltage ref is taken by attaching conductors to each phase,
the Neutral and the ground bar. The digital Meter has a 3-pole
5A breaker in it so the conductors in the load center can be connected to lugs
on the bus bar directly.
Al
Frishman
AeonSolar
(917) 699-6641
- cell
(888)
460-2867
www.aeonsolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To:
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs
Another
key is to remember that this discussion also applies to the conductor between
the main panel and subpanel. In a large PV system, this could result in a pretty
large wire between the two panels, and a significant cost that is often
overlooked. In some cases it makes sense to locate the subpanel close to the
main panel and run multiple sets of smaller wires from the inverters to the
subpanel.
And
because the calculation is based on the first OC protection connected to the
inverters, adding a main breaker (theoretically 80A in this example) in the
subpanel doesn’t change things. Even though this wire would be theoretically
protected by an 80A breaker at each end, you can’t size the wire for 160A / 1.2
= 133.3A. You have to size for 180A/1.2 = 150A. (not that it makes much of a
difference in this example, but it still must be
considered)
At
least that’s how I understand it…
Jason
Szumlanski
Fafco
Solar
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To:
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs
Opps!
My bad,
I was thinking of a single phase system, not the three phase system
shown in the article.
For the
three phase system Kent is correct in counting 180A of supply per
bar.
Mark Frye
Berkeley
Solar Electric Systems
303 Redbud Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To:
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combine multipleinverter outputs
I think
Kent and I agree. For the case where the subpanel is not dedicated a PV
sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 - 50A
breakers.
Mark Frye
Berkeley
Solar Electric Systems
303 Redbud Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To:
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combine multiple inverter outputs
Per 705.12(D) the sub-panel could
be any distribution equipment on the premises. So the question becomes: is the
sub-panel capable of supplying branch circuits or feeder loads? If yes, then the
sum of the breakers (potentially) feeding the bus is 180 amps so a 150-amp
rating is required and the inverters would have to feed the opposite end of the
bus bars. If no, the code is not clear on the requirement, but obviously the
80-amp breaker in the main panel limits the maximum current flowing through the
sub-panel.
Kent Osterberg
Blue Mountain
Solar
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110330/c983f983/attachment-0003.html>
More information about the RE-wrenches
mailing list