I have charged 72 volts on a golf cart type deal, with 2 each morningstar T60
and with 2 each MX 60s But Appolo may work or Classic
the trick is only use the charging function do not connect any communication
cables Grounding is the problem. as one of the controllers is floating. with
its negative terminal at 36 volts. The array has to be set up bipolar. The MX
60 was done with help from the old Outback Crew, back when Chris and Bob were
there. I do not know who you would speak to now. With Morning Star you have to
have the meter for the t-60 to set it up for 36 volts again check with
MorningStar, I can not give you a name. I only now work with Brad
Connect a center tap to the batteries 36 volts connect negative of one
controller to negative of array, connect Positive to 36 volt point of batery.
connect second controller negative to 36 point of battery and positive to 72
volt point.
Also the MX 60 may have changed. the Tri60 may have changed.
Darryl
________________________________
From: Mick Abraham <mick at abrahamsolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Tue, February 8, 2011 10:06:02 PM
Subject: Re: [RE-wrenches] questions about solar charging 72v UPS
Hi, Ron~
The Midnite Classic PV controller shows 72 volt nominal as one of the battery
choices on its menu screen. That's about the only option I know of. Even though
the HV controller from Apollo can accept a similar range of PV input voltage I
think that unit stops at a 48v battery--maybe because of code problems with
battery strings above 50 volts.
For charging a 72 volt lead battery, consider a minimum of 36 X 6 = 216 PV cells
in each charging string. Confirm that "cell count" suggestion with someone who
knows more than I do about the Midnite controllers...such as boB Gudgel who is a
frequent List contributor. I just unboxed my first Classic controller and I look
forward to learning more about this item.
With a 72 volt lead acid battery bank it will be difficult to maintain equal
state of charge on the 36 chemical cells in each battery string. As you know,
Ron, one can only add/remove energy through the whole battery string--barring
new developments--so if some of those critters get out of line it will be tough
to re-establish good discipline.
Jolliness,
Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675
On Tue, Feb 8, 2011 at 8:07 PM, Ron Young <solareagle at solareagle.com> wrote:
Hi All,
>
>
>I recently acquired some UPS units that are a high end portable units (GE
>GT3000). They are nearly new and I would like to rig them up as a standalone
>emergency back-up power source with a solar (or wind) charging option. These
>units have sine wave output and are a double conversion type, i.e. power out is
>isolated from power in by ac to dc to ac conversion. The main problem I have is
>that the battery pack is 72v. It is expandable and I can add up to four
>additional packs to increase the runtime to over three hours at half power (1200
>watts). How do I charge this type of battery pack with solar? Is there a charge
>controller out there that will provide nominal
>72v? http://www.gedigitalenergy.com/PowerQuality/catalog/gtseries.htm
>
>
>Best Regards,
>Ron Young
>earthRight Products - Solareagle.com
>Alternative Energy Solutions ~ Renewable Energy Products
>1-877-925-2929
>blog: http://www.earthrightsolar.tumblr.com
>website: http://www.solareagle.com
>email: sales at solareagle.com
>79F North Third Ave
>Williams Lake, BC
>V2G 2A3
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>
____________________________________________________________________________________
We won't tell. Get more on shows you hate to love
(and love to hate): Yahoo! TV's Guilty Pleasures list.
http://tv.yahoo.com/collections/265
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110209/1c11c9d5/attachment-0003.html>
More information about the RE-wrenches
mailing list