Dave Click daveclick at fsec.ucf.edu
Sun Dec 12 15:05:56 PST 2010


690.35 (D)  The photovoltaic source conductors shall consist of the 
following:
(1) 	Nonmetallic jacketed multiconductor cables
(2) 	Conductors installed in raceways, or
(3) 	Conductors listed and identified as Photovoltaic (PV) Wire 
installed as exposed, single conductors.
***

As soon as you enter a raceway, you can do whatever you like! THWN-2 is 
just fine.


Marco Mangelsdorf wrote:
> I’m starting to use the SMA SB transformerless 8-10 kW inverters.
>
> It appears that the new SMA 6-circuit combiner box is being included
> whenever I order one of these buggers (at least from my distributor).
>
> Does the double insulated PV wire have to be used all the way back to
> the inverter? Or can I get by with just using it to the combiner and
> then transition to the usual TWHN-2 wire?
>
> Thanks,
>
> marco
>
>
>