Nick Soleil nicksoleilsolar at yahoo.com
Mon Oct 18 13:41:11 PDT 2010


Hi Daryl:  
    Unfortunately, the fault would not have been found with a megger because the 
fault occurred after thermal expansion had causes the conduit to separate.  The 
fault probably occurred shortly after the conduits separated.  It appears that 
what would have prevented the incident would have been if the expansion fitting 
on the conduit had been installed correctly, with all of the conduit straps 
allowing some movement.  Also, it sounded (from the report) like the conduit 
fittings were not tightened fully (only hand tight), which contributed to the 
fault.

     This is not typical of the quality I would have expected from this 
manufacturer/ commercial installer.  Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Darryl Thayer <daryl_solar at yahoo.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Mon, October 18, 2010 12:28:57 PM
Subject: Re: [RE-wrenches] Target fire


I keep thinking had the installer routinely megohmed the ground and the "hot" 
they would have known a ground fault existed, and would have repaired.  The 
event would have not happened.  Then the short on the conduit would have triped 
the ground fault detector, and lead to a repair.  No fire.  

 
Again it is installers with knowledge, tools  and skills.
Darryl
 


--- On Mon, 10/18/10, William Miller <william at millersolar.com> wrote:


>From: William Miller <william at millersolar.com>
>Subject: Re: [RE-wrenches] Target fire
>To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>Date: Monday, October 18, 2010, 1:47 PM
>
>
>Andrew:
>
>It may be in the report:  http://mpandc.com/practices/Safety/safety_data.html
>
>William
>
>
>
>
>At 11:30 AM 10/18/2010, you wrote:
>
>
>Does anyone know who installed the infamous Bakersfield Target job?
>>
>>
>>
>>Andrew Truitt
>>NABCEP Certified PV Installer™ (ID# 032407-66)
>>Truitt Renewable Energy Consulting
>>(202) 486-7507
>>http://www.linkedin.com/pub/andrew-truitt/8/622/713
>>
>>
>>
>>"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to 
>>fission. And it just so happens that there's an enormous fusion reactor safely 
>>banked a few million miles from us. It delivers more than we could ever use in 
>>just about 8 minutes. And it's wireless!"
>>
>>~William McDonough
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>>
>>No virus found in this incoming message.
>>Checked by AVG - www.avg.com 
>>Version: 8.5.448 / Virus Database: 271.1.1/3204 - Release Date: 10/18/10 
>>06:34:00
Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985

>-----Inline Attachment Follows-----
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
> 



      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101018/2576432b/attachment-0004.html>


More information about the RE-wrenches mailing list