Hello,
I am having trouble metering  a system with an Outback 3648
serving a
protected loads panel. I need a way to accurately measure
the production.
I have a dual stator 12s meter installed with the "AC in"
coming in the
bottom and out the top and the AC from the inverter going in
the top and
out the bottom with a neutral from the E-panel connected to
the fifth leg.
The meter is not reading anything close to the Outback. Any
ideas would be
greatly appreciated.