[RE-wrenches] RETURN AMP SETTING
Steve Higgins
shiggins at outbackpower.com
Mon Jul 26 09:22:18 PDT 2010
The only way for Outback gear to measure return amps is to incorporate
an FNDC in the installation.
Otherwise then yes you are correct.
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Monday, July 26, 2010 8:02 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] RETURN AMP SETTING
Steve,
Just to make sure I am not missing something, there is no way to
directly set Outback equipment for a particular return amp rate. Rather
one must observe the charge cycle and set the absorption timer
accordingly.
Do have that right?
Thanks,
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com <http://www.berkeleysolar.com/>
________________________________
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steve
Higgins
Sent: Monday, July 26, 2010 6:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] RETURN AMP SETTING
Sorry all... I was out on a little three day vacation.
I usually program return amps setting to usually 2-3% of the overall
battery bank capacity.
Usually and depending on the battery type or manufacure when the current
passing from the charger to the battery drops to this Return amp setting
technically the batteries are charged.
Because batteries are technically buckets of water with holes in them,
they will never stop pulling current, nor will they never be fully
charged. What happens is they start to draw a minimum of charge
current from the charger. This "Maintenance current" usually is
between 2,3,4,5 percent of the overall battery bank capasity.
With the Return amps setting you can get the batteries close to that
charged setting.
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100726/25fe2ac8/attachment-0004.html>
More information about the RE-wrenches
mailing list