[RE-wrenches] AC Coupling to an Endurance wind machine

Darryl Thayer daryl_solar at yahoo.com
Fri Jul 23 14:33:13 PDT 2010


Was Return Amps
Thanks Roy 
I usually leap then look, 
The customer has it already,   I ran it yesterday, on AC couple into the standalone system, I learned a lot.  But it ran, and I am working out some of the surprises I had.  I am building up two inverter boards with the systems to control the excess battery charging.    I hope that Endurance does not get mad at me.  It appears to be very will built machine.  

I am also trying to modify my Dyno to drive the machine, so I can do some controlled testing.   

BTW when the anemometer indicates wind is present, the motor runs to start the blades,  I was measuring up to 6400 watts surge.  After it starts, it is impressive the power output.  I have another install but hope to return with new parts on Wed of next week.  I will keep all informed.   And all ideas are welcome and probably needed.  
Darryl

--- On Fri, 7/23/10, Roy Butler <roy at four-winds-energy.com> wrote:

From: Roy Butler <roy at four-winds-energy.com>
Subject: Re: [RE-wrenches] RETURN AMP SETTING
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Friday, July 23, 2010, 4:04 PM



  
    
    
  Darryl,

    

    You are probably aware of this but the Endurance machines are 240
    VAC induction machines.

    I had asked about their policy on AC coupling their turbines for off
    grid use and they were

    less than enthusiastic.

    

    You might want to touch base with Endurance Wind Power before
    proceeding.

    Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
PA Sunshine Program Approved PV Installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747

www.four-winds-energy.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                

    

    On 7/22/2010 9:09 PM, Darryl Thayer wrote:
    
      
        
          
            I am talking with a
              customer who wants to do a standalone system using an
              Endurance wind machine, solar, and genset.   I have no
              experience with Endurance other than to know it is a good
              machine.  Talking with Magnum today they informed me that
              the MS 4XXX PAE inverter, combined with the ARC remote
              control, and BMK battery monitoring kit can do enhanced
              SOC control.  Has anyone compared this with the Outback as
              I have not used the PAE inverter yet, only the AE
              inverter?  

              Darryl

              

              --- On Wed, 7/21/10, Darryl Thayer <daryl_solar at yahoo.com>
              wrote:

              

                From: Darryl Thayer <daryl_solar at yahoo.com>

                Subject: Re: [RE-wrenches] RETURN AMP SETTING

                To: "RE-wrenches"
                <re-wrenches at lists.re-wrenches.org>

                Date: Wednesday, July 21, 2010, 9:35 PM

                

                
                  
                    
                      
                        That is
                          a good question, I have not an answer, but of
                          course it should be based on the amp hour of
                          the battery bank, absorb charging voltage, and
                          of course the charging source in the case of
                          generators.  Following Ron's advise start at
                          C/5 for SOC less than 50% then C/10 till about
                          70% SOC and then C/15 till 80% then C/20 to 90
                          %. the problem we have no way to set these
                          values, Perhaps Ron could give is a routine? 
                          The closet to SOC charging is the Outback and
                          then the Magnum but both miss the goal.  

                          

                          --- On Wed, 7/21/10, Dana <dana at solarwork.com>
                          wrote:

                          

                            From: Dana <dana at solarwork.com>

                            Subject: [RE-wrenches] RETURN AMP SETTING

                            To: "'RE-wrenches'"
                            <re-wrenches at lists.re-wrenches.org>

                            Date: Wednesday, July 21, 2010, 5:54 PM

                            

                            
                              


                              
                                As the % of full charge
                                    is related to the of degree
                                    absorption
                                    & gravity [the denser & more
                                    charged acid descending, and lighter
                                    acid rising]
                                    @ what point in the absorption would
                                    be prudent to stop charging?
                                  
                                I used to cut off the
                                    charge on the Trace SW series at 12
                                    “return
                                    amps”, VS. the factory default I
                                    think was at 5 amps.  This has &
                                    continues to work well but I never
                                    had anyone really answer this
                                    function
                                    clearly.
                                  
                                Is there a battery
                                    manufacturer  or wrench that would
                                    care to comment on the:  
                                The minimum “Return”
                                    amps to disconnect for a “full”
                                    charge?
                                OR
                                The time required per
                                    100 AHR after reaching the
                                    Absorption
                                    point setting for the mix to occur?
                                  
                                I realize that battery
                                    construction, battery condition, age
                                    and temperature and the current
                                    power usage will also play into this
                                    factor and
                                    it may not be a simple answer.
                                  
                                  
                                  
                                  
                                  
                                
                                   Dana
                                      Orzel
                                    
                                  Great
                                      Solar Works, Inc
                                  E -
                                      dana at solarwork.com
                                  V -
                                      970.626.5253
                                  F -
                                      970.626.4140
                                  C -
                                      970.209.4076
                                  web -
                                      www.solarwork.com
                                  Responsible
                                      Technologies for Responsible
                                      People since
                                      1988"
                                
                                  
                                
                                  
                                    From:
                                        re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org]
                                        On Behalf Of Mark
                                        Frye

                                        Sent: Wednesday, July 21,
                                        2010 4:25 PM

                                        To:
                                        Allan at positiveenergysolar.com;
                                        'RE-wrenches'

                                        Subject: Re:
                                        [RE-wrenches] Propane Generator,
                                        Dual Outback Inverters
                                  
                                
                                  
                                Allen,
                                 
                                Can I infer that if you are
                                    shutting off the gen before charge
                                    rates drop in absorption that you
                                    are
                                    running only briefly in the absorb
                                    phase? Or do your charge currents
                                    remain
                                    high through out an extended
                                    absortion phase?
                                 
                                Perhaps you have plenty of PV
                                    which you rely upon to bring the
                                    batteries up through the absorption
                                    phase,
                                    once the gen is shut off.
                                 
                                I would be interest to learn
                                    more
                                    about your approach to this.
                                 
                                Thanks,
                                 

                                  Mark
                                    Frye
                                  

                                  Berkeley
                                    Solar
                                    Electric Systems 

                                  303
                                    Redbud Way
                                  

                                  Nevada
                                    City,  CA 95959 

                                  (530)
                                    401-8024
                                  

                                  www.berkeleysolar.com  
                                
                                   
                                
                                  
                                
                                  
                                
                                From:
                                    re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org]
                                    On Behalf Of Allan
                                    Sindelar

                                    Sent: Wednesday, July 21,
                                    2010 3:17 PM

                                    To:
                                    re-wrenches at lists.re-wrenches.org

                                    Subject: Re: [RE-wrenches]
                                    Propane Generator, Dual Outback
                                    Inverters
                                The Onan RS20000 shown in the
                                  generators article in HP
                                  131 page 98 has performed flawlessly
                                  as backup support to an Outback
                                  quad-stack
                                  of VFX3648s. Differences, however, are
                                  that this 20kW gennie charges four
                                  inverters, rather than two; the
                                  elevation is 6,600 feet for about a
                                  20% output
                                  deration; there are no huge loads
                                  above charging draw; and the client is
                                  aware
                                  enough to shut it off before
                                  absorption reduces the charge rate -
                                  all different
                                  conditions than you have described, as
                                  the gennie is usually fully loaded and
                                  running in balance.

                                  

                                  Darryl is right about the amount of
                                  words necessary.
                                
                                  Allan
                                      Sindelar

                                      Allan at positiveenergysolar.com

                                      NABCEP Certified Photovoltaic
                                      Installer

                                      EE98J Journeyman Electrician

                                      Positive Energy, Inc.

                                      3201 Calle Marie

                                      Santa Fe, New Mexico 87507

                                      505 424-1112

                                      www.positiveenergysolar.com
                                
                                No virus found in this
                                    incoming message.

                                    Checked by AVG - www.avg.com

                                    Version: 9.0.851 / Virus Database:
                                    271.1.1/3008 - Release Date:
                                    07/21/10
                                    00:36:00
                              
                            
                            

                            -----Inline Attachment Follows-----

                            

                            _______________________________________________

                              List sponsored by Home Power magazine

                              

                              List Address: RE-wrenches at lists.re-wrenches.org

                              

                              Options & settings:

                              http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                              

                              List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                              

                              List rules & etiquette:

                              www.re-wrenches.org/etiquette.htm

                              

                              Check out participant bios:

                              www.members.re-wrenches.org

                              

                            
                          
                        
                      
                    
                  
                  

                
                

                -----Inline Attachment Follows-----

                

                _______________________________________________

                  List sponsored by Home Power magazine

                  

                  List Address: RE-wrenches at lists.re-wrenches.org

                  

                  Options & settings:

                  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                  

                  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                  

                  List rules & etiquette:

                  www.re-wrenches.org/etiquette.htm

                  

                  Check out participant bios:

                  www.members.re-wrenches.org

                  

                
              
            
          
        
      
      

      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


    
  

-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100723/b14c2446/attachment-0004.html>


More information about the RE-wrenches mailing list