Chris Worcester chris at solarwindworks.com
Wed Jun 16 12:05:17 PDT 2010


Hi Ray,

Good points on the aging pump syndrome for sure. I like the idea of the
added Franklin soft start, but this feeds a gravity tank up the hill from
the home so can't use the constant pressure side.

I have the load start set at 24.2V for 24 hours, 24.0V for 2 hours, and
23.8V for the 2 minute setting to keep the batteries up. LBCO at 22.6V. I'd
try this first with the extra inverter running the well pump and raise it
sparingly if required to keep the spread from hitting the LBCO.

The Generac has been giving them an error message, and the other thread
about the "Gen Set problems" is timely here!

 

Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com <http://www.solarwindworks.com/> 
chris at solarwindworks.com
"Proven Energy Solutions"

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Tuesday, June 15, 2010 12:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

 

I've run a 3 Hp pump on a pair of Outback inverters, but it's not a done
deal. As the pumps age, they start getting stickier (read more start up
current needed to get them going) and wells often have silt which builds up
in the pipe and pump, adding to the start up surge.

I recently had a system with a one HP pump, that ran for years on an SW4024,
but when we went to grid tie with an Outback, it overloaded. The cure was a
fancy controller from Franklin that operates a regular submersible pump as a
constant pressure pump with no start up surge.

Then you'll find out how good your battery bank is, as a 3 HP pump will pull
the battery voltage down rapidly. I'd have the Generac set to fire up at a
higher than normal voltage, well before the inverters cut out.

Too bad its a Generac.

 

R. Walters

ray at solarray.com

Solar Engineer

 

 





 

On Jun 15, 2010, at 12:24 PM, Chris Worcester wrote:





Hello offgrid Wrenches,

I just inherited an off grid system with one VFX3524 inverter running the
home loads, and a 17kW Guardian Generac they use for charging (through an
X-240 back into the inverter) & to run their Franklin 3hp 240 VAC well pump,
S. F. max amp 17.0 ( rated on its controller)

This is a really convoluted system as they have another 120/240 VAC
Transformer to have the inverter talk to the 240 volt signal the gen set
needs to see. Yikes.

So I am proposing to add a second inverter if it can run the well pump and
eliminate the extra transformer. This will also reduce gen set run time in
half while battery charging, a big plus with the nice 24V Hawker battery
bank, 1020 AH at the 6 hour rate.

There aren't any other unusual large AC loads in the home, just the fridge,
washer, computer, and such. LPG for cooking, water heating, clothes dryer.

Thanks in advance for all ideas here!

 

Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com <http://www.solarwindworks.com/> 
chris at solarwindworks.com
"Proven Energy Solutions"

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100616/35c728a0/attachment-0004.html>


More information about the RE-wrenches mailing list