[RE-wrenches] SWH - mixing valves
Kelly Keilwitz, Whidbey Sun & Wind
kelly at whidbeysunwind.com
Thu May 20 08:31:18 PDT 2010
Doug,
I HAVE had tank (SS) temps in excess of 180˚, but rarely. These valves
are the Honeywell Sparcomix AM series. I don't see any temperature
limitations listed in the specifications.
-Kelly
Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
kelly at whidbeysunwind.com
360-678-7131
On May 19, 2010, at 6:48 AM, Doug Wells wrote:
> Kelly,
>
> I have also seen mixing valves get leaky over time. Many mixing
> valves are designed for controlled input from a boiler at steady 140
> degree temps. It is not uncommon for SHW tanks to reach 180+
> degrees in certain conditions. If exposed to these higher temps the
> valves can begin to loose accuracy. Usually they are designed to
> "fault" into the cold position, so the begin to leak in a little
> cold and the client will complain about low temps at the faucet/
> shower.
>
> Doug Wells
> The Solar Specialists
> Morrisville, VT 05661
> (p) 802-223-7014
> (c) 802-498-5856
> www.thesolarspecialists.com
>
> On May 19, 2010, at 2:14 AM, Kelly Keilwitz, Whidbey Sun & Wind wrote:
>
>> Thermal wrenches,
>> I'm having an ongoing issue with mixing valves in my own system not
>> keeping a steady mix domestic HW temperature as the tank
>> temperature varies with solar heating. If I set it for (say) 122˚F
>> mix when the tank is 135˚, it seems to hold that differential at
>> all tank temps - i.e. when the tank is hotter the mix is too hot
>> (sometimes dangerously so), and when colder the mix is too cold for
>> a comfortable shower. Thus, I need to change the setting all the
>> time.
>>
>> I'm now using a Honeywell valve with a 90˚ - 145˚ range. This is a
>> replacement for a valve with a wider range that acted the same way.
>> Any ideas, suggestions for better valves, or....?
>>
>> This has me wondering how many of our SWH customers are
>> experiencing a similar thing, but just aren't bothered enough to
>> say anything. We seem to have encountered many plumbing situations
>> where the mixing valve allowed weird backflow or siphoning
>> situations to mess with system operation, especially with HW
>> recirculation. I thought I had all such causes eliminated on my
>> system, but maybe not.
>>
>> Thanks for sharing your experience with such matters.
>> -Kelly
>>
>> Kelly Keilwitz, P.E.
>> Whidbey Sun & Wind
>> Renewable Energy Systems
>> kelly at whidbeysunwind.com
>> 360-678-7131
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list