Hi Jeff,

I probably should mentioned that many of our float switch wire runs 
exceed 3,000 feet from tank to Cu200.
We use shielded, direct burial rated 18/2 cable, bury the wire and 
ground the drain wire at the controller.

So with those "long distance" systems, do you think a relay would work? 
It just doesn't seem feasible to run
coil voltage that far. That's why we've been relying on the CU-200 
microprocessor to do the job. Also, I
don't like to run anything but the pump off a PV direct system.

As for the pressure tank/ switch option, we do have a few of those out 
there and I agree, they work fine.
But on some of our systems the vertical rise between the pump and 
storage tank is over 300 feet. That's
about 130 psi and those pressure tanks wouldn't like that too much. And 
for various design reasons, a check
valve on the main feed line isn't feasible, so we ruled out the pressure 
switch option on these "long distance"
systems.

I also like to keep things as simple as possible where livestock water 
is concerned. Farmers have so many
maintenance items on their list now, I hate to add more. So at first 
look, the Cu200 seemed to be the ticket.

Thanks for the info!

Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV&  wind installer
PA Sunshine Program Approved PV Installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747

www.four-winds-energy.com

Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.

===============================================
The 6th Annual Small Wind Conference
A Gathering of small wind industry stakeholders
June 15 and 16, 2010
Stevens Point, Wisconsin
info at smallwindconference.com
http://www.smallwindconference.com


On 4/22/2010 4:20 PM, Jeff Oldham wrote:
> Hi Roy,
>
> You do have a choice about controllers, as I mentioned I use off-the-shelf components. For your need you have at least 2 sweet options - 1) get a relay to switch the pump power and use a float switch to control the coil, go with a SSR for even higher reliability.  This is a $50 substitute for a $300 CU-200. 2) Use a Cla-val at the tank and a pressure switch and 2gal press. tank at the pump. This works at any distance w/o control wires and is fully hydraulic and highly reliable plus this valve does not throttle as it reaches full. This is my control of choice if the distance between pump and tank is much over 400', cost must be considered as this is about a $700 setup.
>
> -jeff o
>
> > From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative SOLutions
>
> ____________________________________________________________
> Penny Stock Jumping 2000%
> Sign up to the #1 voted penny stock newsletter for free today!
> http://thirdpartyoffers.juno.com/TGL3131/4bd0afe9e1274a5860st03vuc
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>    




More information about the RE-wrenches mailing list