Andrew,
I have done this for multiple installs, most recently on a commercial
three phase 240 install (with 6 SMA 7000s) and a residential two
circuit Enphase install. The plans were submitted to the AHJ and
approved in both cases without question. I labeled these per 705.10
and 690.64.
The commercial install was as you suggest to simplify the grid
connection. The residential Enphase install was done to provide a
single point of metering for the system.
I hope this helps
Carl Adams
SunRock Solar
On Tue, Jan 12, 2010 at 2:35 PM, William Miller <william at millersolar.com> wrote:
> Andrew:
>
> It is not in the code. It is an argument you make to your own AHJ.
>
> William
>
>
>
> At 10:57 AM 1/12/2010, you wrote:
>
> Team wrenches - I feel like I've seen a provision in the Code for installing
> a sub-panel to aggregate PV inverter outputs for the purpose of simplifying
> the actual grid connection (such as for a line-side tap) but I can't find it
> in 690. I also seem to remember specific verbiage that needs to be on the
> panel along the lines of "PV circuits only. Do not add load breakers." to
> ensure compliance with 690.64(B). Does anyone know where I can find this
> info in the NEC?
>
>
> Andrew Truitt
> Standard Solar Inc.
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
More information about the RE-wrenches
mailing list