Hi Bob,
 
Maximum height to the top of handle is 6'7". Can't recall the millimeter
conversion off the top of my head... Oh, wait! My tape is in inches, anyway.
 
Minimum height is a judgement call. Your judgement and the AHJ's judgement.
 
Look around. Is there anything that can/will interfere with or damage the
switch? Sprinklers, pallet-jacks, foot traffic? Next thing i look for is
"where is it the most functional"? Visible and reachable is more valuable
than trying to use a short piece of conduit and wire. i also look at
importance... If there is one switch that controls a high hazard source, for
instance... You want it in a prominent location. A switch that may need to
be operated in a emergency shouldn't be mounted too low. 3' or higher, for
sure. The closer to eye level, the better.
 
It's always a challenge looking for the best arrangement of equipment with
complex systems. One thing i try to do is visualize the space and
arrangement from the perspective of entering the area. What if somebody is
not too familiar with the equipment and it's an emergency? Can they spot and
operate the swiches they need easily? i have had some very good solutions
appear from this exercise over the years. Solutions that my brain didn't see
from "straight on". 
 
Hope you find the right mix, Bob.
 
Two Pines and a Hammock,
 
matt lafferty
  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Friday, November 26, 2010 5:35 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Code switch heights


Bob,
This came up once years ago. I recall that there is no minimum height in the
Code for your application.



Allan Sindelar
 <mailto:Allan at positiveenergysolar.com> Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/> 


On 11/26/2010 5:11 PM, bob ellison wrote: 

I am looking at installing 4 inverters in a system, 1 on an e panel and 2 SW
4048's and also a SW plus. So its an interesting mix, 3 are just to cut the
generator run time for the diesel generator.



I am trying to find the allowable range for switch heights for all the gear.

Seems the upper limit is about 6' but I am unsure on the lower limit.



Any ideas?



Thanks,

Bob Ellison

 
 