[RE-wrenches] Code reference needed

August Goers august at luminalt.com
Tue Oct 26 06:53:20 PDT 2010


Allan -



I believe you are referring to NEC 110.26(A)(3) Height of Working Space.



They talk about the 6" plane in that section.



-August





August Goers



Luminalt Energy Corporation

1320 Potrero Avenue

San Francisco, CA 94110

m: 415.559.1525

o: 415.641.4000

august at luminalt.com



*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Allan Sindelar
*Sent:* Monday, October 25, 2010 11:12 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Code reference needed



Wrenches, what's the actual Code reference location for the requirement that
service equipment be within 6" of the same plane? I couldn't find where I
expected it in Art. 110.
Thanks, Allan

-- 