[RE-wrenches] paralleling FM-60's
Mick Abraham
mick at abrahamsolar.com
Wed Oct 20 09:13:36 PDT 2010
This sounds like a job for a single Apollo T-100. If you do that, Jay,
be sure to wire the solar strings with somewhat more than 36 PV cells
for every 12 volts of battery.
Jolliness,
Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675
On Wed, Oct 20, 2010 at 10:00 AM, Kent Osterberg <kent at coveoregon.com> wrote:
> William,
>
> There are some issues with putting the charge controller at the other end of
> the feeder:
> 1. The advantage of a higher voltage feeder is lost.
> 2. The voltage drop in the feeder will mess up the charge controller's
> absorption and float set points. Say there is only 1% drop in the deeper,
> that's 0.14 volt for a 12 volt system (2x for 24 or 4X for 48 volts). If
> the feeder loss is more ... You could raise the set points at the regulator
> to offset the feeder loss, but the loss in the feeder is not a constant.
> 3. The charge controllers are not NEMA 3 rated, they need to be inside.
>
> Kent Osterberg
> Blue Mountain Solar
>
>
>
>
> William Miller wrote:
>
> Jay:
>
> Bad idea. The differences in tolerances within components will make one
> work harder than the other. They will never balance. Why not put the
> charge controllers at the other end of the feeder?
>
> William Miller
>
>
>
> At 08:06 AM 10/20/2010, you wrote:
>
> HI All,
>
> Say anyone ever paralleled mx/fm-60's?
>
> I have a unique situation that would be very expensive to pull additional
> wire however the existing wire is large enough to need 2 fm-60s'
>
> If I put a diode between them so they don't feed each other any problems
> that anyone knows of?
>
> thanks,
>
> jay
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
More information about the RE-wrenches
mailing list