[RE-wrenches] Battery capacity testers
toddcory at finestplanet.com
toddcory at finestplanet.com
Mon Oct 4 00:22:55 PDT 2010
I know many on this list disagree, but this sounds SO typical for sealed batteries. It is why I never use em... never! If they are 5 years old, you are probably at the limit of their life. Replace em with flooded lead calciums and your customers (and you) will be happy for 20+ years.
my .o2
Todd
On Sunday, October 3, 2010 9:28pm, "North Texas Renewable Energy Inc" <ntrei at 1scom.net> said:
I have a customer with a set of 24 Concord PVX-6480s that have twice failed during grid outages during the night. No large loads are on the critical load panel and, since it's at night when they drop to 50% dod, I'm not sure what's up with them. I plan on cleaning and retightning all the cable connections first to eliminate that possibility then checking VOC of each cell.
Eventually we'll install a 25 kW genset but my first task is to find out the state of the batterys. The system turns five next spring so I don't think they are near an early death. The BOS is 2 Sunny Island 4248s with upgraded chipsets and the charger is set to spec though that may need to be bumped up. The only culprit I suspect is the high summer temperatures in this unconditioned equipment room.
Finally it may be time to invest in a capacity tester. What brand is popular among those Wrenches with lots of experience in diagnosing a batterys health? The Concord DC5000 only comes in 12 & 24 V models and these are 2V cells.
Thanks as always
Jim Duncan
North Texas Renewable Energy
486 W.N. Woody Road
Azle Texas 76020
NABCEP Certified Solar PV
Installer No.31310-57
TECL 27398
[mailto:ntrei at 1scom.net] ntrei at 1scom.net
817.917.0527
[http://www.ntrei.com/] www.ntrei.com
Sent from Finest Planet WebMail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101004/3843e013/attachment-0003.html>
More information about the RE-wrenches
mailing list