[RE-wrenches] Thermal isolation for battery bank

Dana dana at solarwork.com
Sat May 1 09:53:21 PDT 2010


To thermally isolate the battery bank in un-heated locations we use 1½” blue or pink board under ¾” exterior ply wood on top to set the battery bank on. It will settle a hair but this has worked for years in many places. 

 

Thanks,  Dana Orzel

 

Great Solar Works, Inc

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

Responsible Technologies for Responsible People since 1988"

 

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Saturday, May 01, 2010 9:47 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Ideal platform for flooded type batteries: opinions wanted

 

As you know, cold floors reduce battery charge.  We use a support "shelf" made of pressure treated 2 x 4 on EDGE, separated by 3/8" pressure treated plates every 2 feet, using 8 foot long boards.  This 16" wide by 8 foot long shelf is placed on standard concrete blocks spaced every 2 or 3 feet, keeping the shelf  8" above the floor.  This puts the battery fill caps at a nice level for re-fill, and the bottoms off the cold floor which allows good air flow.  An occasional acid spill may cause some minor issues, but we have these shelves in systems now over 15 years old with no problems.  The are also easy to site build.