Friends:
We field tested the concepts this morning and the answer is "yes"
(inter-row shading in portrait mode: bad -- in landscape mode: less bad).
William
At 08:40 PM 4/22/2010, you wrote:
>Friends:
>
>99% of the time, we install modules in portrait mode. We find ourselves
>installing a set in landscape with some short inter-row spacing, due to
>roof vents. We are using Solarworld SW230 modules.
>
>It is my understanding that shading the short edge of this type of module
>is much more detrimental to the output than shading a long edge. This is
>because of the manner in which the cells within the module are arranged in
>series. I understand that one string is on the bottom half of a module
>and the other on the top half of a module in the landscape
>orientation. In order for the module to cease power production, you have
>to shade at least one cell from each of the two internal
>strings. Therefore, you need to shade more than half of a module in the
>landscape mode before the module before the output declines drastically.
>
>Is my understanding here correct? I will be testing this tomorrow if
>weather permits.
>
>Thanks in advance.
>
>William Miller
>
>
>Please note new e-mail address and domain:
>
>William Miller
>Miller Solar
>Voice :805-438-5600
>email: william at millersolar.com
>http://millersolar.com
>License No. C-10-773985
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>No virus found in this incoming message.
>Checked by AVG - www.avg.com
>Version: 9.0.814 / Virus Database: 271.1.1/2829 - Release Date: 04/22/10
>11:31:00
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100423/3f3ce2c4/attachment-0003.html>
More information about the RE-wrenches
mailing list