[RE-wrenches] Interstate UL-16 HC problem
bob
reellison at gmail.com
Tue Jun 29 03:52:37 PDT 2010
I have 2 systems that I am trying to correct that another local dealer has
installed.
This one is 2 strings of (8) UL-16 HC Interstate Batteries, 16 batteries
total.
We cannot get the batteries to charge over 1.225 despite discharging them
and generator charging them till everything shut down.
This is a 48 volt system with a Magnum 4448 inverter.
He also has (6) 175 watt Solar World panels on a manual tracker. (spends all
day tracking the sun) He is adding 2 more this summer. The controller is an
MX-60.
I have moved the Magnums settings to 1600 AH battery bank size to allow for
the inverter to have a longer absorb time to help it finish charging and get
to a full battery.
It's not working; we have 1 cell at 1.240 and the rest at 1.225.
These have not been cycled hard if at all, I am going to suggest that he
cycle them several more times to see if anything improves after that
The other system has the same problem with a different inverter! So it's not
inverter related, but I am at a loss.
I have not used Interstates before and want to stay away from them in the
future.
Any other suggestions?
Thanks,
Bob Ellison