[RE-wrenches] [Fwd: Re: DC wire sizing]
boB Gudgel
boB at midnitesolar.com
Sat Apr 3 13:57:59 PDT 2010
Forwarding a message from Robin Gudgel...
Robin Gudgel wrote:
> The CBI QY series of DC breakers have an arc shoot that is required to
> quench a DC arc. This breaker would work just fine as an AC breaker although
> is not marked as such. I am not sure if the AC breakers (QL, QZ and QZD
> series) have the arc shoot. I was told years ago by CBI that the AC and DC
> breakers are built the same, but I had never broke one open to see if the
> arc shoot is present on AC breakers until today. The AC breakers do in fact
> have the same arc shoot as the DC breakers. CBI just marks the outside of
> the breakers differently. You don't want to get called on the AC vs. DC
> issue by an inspector because you are going to lose that battle. It makes
> things a bit confusing to have a DC breaker in an AC circuit even though
> they are identical inside. I believe Allan Sindelar was in the field and had
> a situation where it saved a bunch of time and hassle to use a QY breaker
> instead of a QL that he did not have on hand. I had told him that the DC
> breaker would function just fine as an AC breaker. That installation was
> safe, but an inspector would probably make you change to an AC breaker.
>
> I remember years ago seeing in print that a Hydraulic/Magnetic breaker could
> be used at 100% duty rating where as a thermal breaker could only be used at
> 80%. I have searched and searched to find this written explanation again to
> no avail. I thought it was in the NEC, but I now believe I was wrong. If the
> NEC does not allow the use of H/M breakers to be used at 100% duty cycle,
> then it just is not allowed. It is true that the H/M breakers are not
> affected by temperature like thermal breakers are, but that in itself
> doesn't overrule the NEC. I personally have been spreading this myth to
> hundreds of installers for 10 years. I now believe I was wrong. Sure wish I
> could find that written explanation from years ago! Perhaps it came from CBI
> or some other circuit breaker manufacturer? (see below) Maybe an old version of the NEC?
> The NEC is the top authority, so please use the same de-rating guidelines
> for CBI as for thermal breakers.
> Sorry for perpetuating this widely accepted myth.
>
PS. Robin found this and thinks that this may have been one of the
texts but still
does not override NEC requirements
>From Heinamann:
Continuous operation at 100%current.
There is no such assurance with a thermal device, which may
fail to carry rated current when subjected to above normal ambient
temperatures. A Heinemann breaker rated at 20 amperes, for example,
will sustain 20 amperes, even at elevated temperatures. Derating
and other forms of temperature compensation are unnecessary.
> Robin Gudgel
> MidNite Solar
>
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] DC wire sizing
> Date: Fri, 02 Apr 2010 16:35:49 -0600
> From: Allan Sindelar <allan at positiveenergysolar.com>
> Reply-To: Allan at positiveenergysolar.com, RE-wrenches
> <re-wrenches at lists.re-wrenches.org>
>
>
>
> Yes, they are 100% duty rated. Also, a little-known fact about the CBI
> breakers used by Midnite and Outback, gleaned from conversations with
> Robin Gudgel: because of this hydraulic/magnetic construction, all are
> capable of controlling both AC and DC, even if not listed as both.
>
> *Allan** Sindelar*
> Allan at positiveenergysolar.com <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
>
>
>
> robert ellison wrote:
>
>> I believe that the breakers from CBI, Midnite and Outback are
>> hydraulic / magnetic and may be operated at 100% While the derating
>> applies to all others that are Thermal / magnetic,
>>
>> Bob
>>
>> On Fri, Apr 2, 2010 at 11:14 AM, Kent Osterberg <kent at coveoregon.com
>> <mailto:kent at coveoregon.com>> wrote:
>>
>> Erika,
>>
>> You should refer to NEC 690.8 this information. There are two
>> issues that contribute to the 1.56 factor. First is that the
>> maximum current from the PV array is considered the short circuit
>> current multiplied by 1.25 to account for higher than standard
>> irradiance such as cloud edge effect, high altitude, and high
>> operating temperature. The second multiplier of 1.25 is because
>> PV current is considered to be continuous. All conductors (and
>> breakers) operating continuously (over three hours I believe) that
>> are subject to NEC rules are limited to 80% of the ampacity in
>> Table 310.16. The two 1.25 factors equals 1.56.
>>
>> For normal operation, wires selected under this criteria are
>> conservatively rated. But it is also the objective of the NEC to
>> design power systems in a manner that they will remain safe under
>> abnormal circumstances.
>>
>> Kent Osterberg
>> Blue Mountain Solar, Inc.
>>
>>
>>
>>
>> Erika M. Weliczko wrote:
>>
>>> To my understanding the 156% on PV source and output circuits is
>>> related to the ability of PV to deliver more than rated and be
>>> continuous.
>>>
>>> Therefore, the wire has to be able to carry this current, so now
>>> the temperature and fill corrections are applied to find the wire
>>> capable of the 156%.
>>>
>>>
>>>
>>> I am in a debate where the question is why correct for temp and
>>> fill on 156% of ISC and spend all that extra money when the
>>> normal operating is at Imp. Or why correct the 156% but why not
>>> correct the Isc or Imp.
>>>
>>>
>>>
>>> I am going to stick to the fact that the circuit has to carry the
>>> 156% under all conditions.
>>>
>>> Thoughts?
>>>
>>>
>>>
>>> Erika
>>>
>>>
>>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>
>>
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
>
More information about the RE-wrenches
mailing list