[RE-wrenches] The Demise of melodrama in this thread
Kirk Herander, VSE
kirk at vtsolar.com
Tue Sep 14 04:52:50 PDT 2010
"The technician dies"? - one would hope a person would have the sense to
wear safety gear, per OSHA and NFPA standards, when debugging a ground
fault.
Kirk Herander
Vermont Solar Engineering
802.863.1202 fax 802.863.7908
VT RE Incentive Program Partner
NYSERDA Incentive-eligible Partner
NABCEPTM Certified Installer
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Tuesday, September 14, 2010 1:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] The Demise of WEEB
Andrew:
You make a very good point in 2) below, however there is one step missing:
If a ground fault is occurring, the technician will eventually need to look
under modules to find the fault. This is the reason the top-down clips will
be loosened. If the module is grounded with #6 wire, the wire will prevent
the module from being lifted. Therefore, the lug will also be loosened,
un-grounding the module -- creating the unsafe condition you described.
WEEB clip or WEEB lug, the technician dies.
Should we invent a WEEB jumper cable to maintain module bond while the
modules are being lifted?
William Miller
At 07:44 PM 9/13/2010, you wrote:
2) My biggest concern with the WEEB Clip is that the moment a top-clamp is
loosened the module is no longer grounded!!! To me that is not a good
grounding method. Mr Wiley is obviously a talented inventor and he makes a
strong argument for the quality of the bond that the WEEB Clip provides when
the clip is installed properly and all mounting hardware is properly
torqued. What I don't understand is the argument that this is as safe of a
product as a properly installed outdoor rated lug for the service tech who
has to work on that array.
A tin-plated copper lug with a stainless steel set screw will last. A
service tech working on a faulted array that was grounded with WEEB Clips
might not.
Andrew Truitt
Free agent
Golden, CO.
-------------- next part --------------