[RE-wrenches] The Demise of WEEB
Keith Cronin
electrichi01 at yahoo.com
Mon Sep 13 10:17:46 PDT 2010
Perhaps in the future, we can go with a composite frame and remove the grounding
challenge altogether?
Carbon fiber would be spectacular, minus the cost.
________________________________
From: R Ray Walters <ray at solarray.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Mon, September 13, 2010 7:14:36 AM
Subject: Re: [RE-wrenches] The Demise of WEEB
I didn't do the original install, and I couldn't ID the lug because of the
corrosion.
I believe everyone is correct that this isn't the DBT rated lug, though.
Another reason to use the WEEB: a crew can't accidentally install the wrong
(but almost identical, when new) lug.
I'm sure the non-DBT lugs got mixed together in a bin at some point.
R. Walters
ray at solarray.com
Solar Engineer
On Sep 12, 2010, at 5:41 PM, Jamie Johnson wrote:
That looks like a tin plated aluminum lug (aluminum corrosion) with a plated
steel screw (rusted screw).......
>
>Here is an explanation of the differences between both ILSCO GBL 4 lugs from
>John Wiles Code Corner in Homepower issue 102
>
>"The Ilsco GBL-4DBT is a lay-in lug made of solid copper, which is then
>tin-plated. It has a
>stainless steel screw to hold the wire. The lug accepts a #14
>(2 mm2) to #4 (21 mm2) copper conductor. It is listed fordirect burial (DB) and
>outdoor use and can be attached to
>aluminum structures (the tin plate). The much cheaper Ilsco
>GBL-4 lug looks identical, but is tin-plated aluminum, has
>a plated screw, and is not listed for outdoor use."
>
>Jamie Johnson
>NABCEP Certified Solar PV Installer #031310-118
>General Manager
>SOLAR POWER ELECTRIC
>EC13001765
>
>-------- Original Message --------
>>Subject: Re: [RE-wrenches] The Demise of WEEB
>>From: "Peter Parrish" <peter.parrish at calsolareng.com>
>>Date: Sun, September 12, 2010 6:50 pm
>>To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
>>
>>Are you sure that's a ILSCO GBL-4DBT lug? I am pretty sure the set screw is
>>not SS, which it should be to be the genuine part.
>>
>>- Peter
>>
>>
>>Peter T. Parrish, Ph.D., President
>>California Solar Engineering, Inc.
>>820 Cynthia Ave., Los Angeles, CA 90065
>>CA Lic. 854779, NABCEP Cert. 031806-26
>>peter.parrish at calsolareng.com
>>Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>>
>>
>>
>>-----Original Message-----
>>From: re-wrenches-bounces at lists.re-wrenches.org
>>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of R Ray
>>Walters
>>Sent: Sunday, September 12, 2010 3:10 PM
>>To: RE-wrenches
>>Subject: Re: [RE-wrenches] The Demise of WEEB
>>
>>A picture is worth a thousand words, (hopefully this will upload)
>>Here's a traditional Ilsco Lug after less than 5 years near the ocean:
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>>
><bottom.letterhead> _______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100913/53950552/attachment.htm>
More information about the RE-wrenches
mailing list