Hi Jim,
I like using one of the design emulators for just this reason. PVSYST and PVSOL. You can model each scenario and see how the numbers crunch. You import historical weather data for the region to get as accurate as possible.
You mention the silver painted roof, these emulators allow you to input albedo affects, too.
Both packages offer free trial periods, so you could run just this case for free. If you like them then you spend the money for the license.
-Wes Kennedy
NABCEP certified PV Installer
303-653-3073
--- On Mon, 4/19/10, Jim MacDonald <jmac at solaresystems.com> wrote:
From: Jim MacDonald <jmac at solaresystems.com>
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Monday, April 19, 2010, 5:40 PM
SB8000US only good for 480 Vac, we’re tying in at 208.
11 strings has been calc’d to be OK (<600vdc) for record low -4
fahrenheit (-20 celsius).
I think the big concern as mentioned is getting the Voc high
early in the AM to wake the inverter up, also maintaining the Vmp later in the
day to keep it running for as long as possible into the late afternoon/
evening.
Will those extra kWh gleaned in the early AM/ late PM over the
course of 365 days be more than the kWh clipped during peak production times
with the 9.075 kWdc?
NYC average summer highs between 79 and 84 fahrenheit early
june-late august. Sunlink rack @ 10° on a silver-painted built-up
roof.
Time-of-use utility $ peak-shaving is not an issue here.
Thank you
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Darryl
Thayer
Sent: Monday, April 19, 2010 5:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod
per string?
The temperature correction is the concern. I have
heard lots of stories of inverters dieing when it gets to cold. Look in
the code book 690.7 at the temperature correction table. Go to
weather.com and find your record low temperature. Find you Tc factor
and will your senerios work? I have heard from a sunny boy rep that it
is OK to over power by 1.25%
darryl
--- On Mon, 4/19/10, Dana <dana at solarwork.com> wrote:
From: Dana <dana at solarwork.com>
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
string?
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date: Monday, April 19, 2010, 4:31 PM
Many times we
switch to another module manufacturer as one will not fit or another inverter
manufacturer.
PVPowered has a
more relaxed window and we have had fine success with them when SMA does not
fit.
Cold is the
dictator and the 600 VDC threshold.
Thanks, Dana Orzel
Great Solar Works, Inc
web - www.solarwork.com
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
"We have been slow to give up
on the myth of the Earth's generosity.
Rather grandly, we have overdrawn
our accounts."
Barbara Kingsolver - Water is life.
From:
re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jim
MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: RE-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
string?
For a straight grid-tie system@ 10 degree tilt, 180
azimuth, zero/little shade, NYC avg 4.29 kWh/m²/day.
Feed an SMA7000 with (3) strings of 11 Suntech STP275’s
[9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac
inverter.
Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp
The tradeoff would be power clipping at/around noon in the
sunny months in the 9.075 kW scenario;
Inverter sleeping late every morning and retiring early in
the evenings in the lowered voltage scenario.
Trying to figure out which would yield more kWh at the end
of the year.
Any ideas appreciated,
thanks
Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.com
No
virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10
00:31:00
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100420/5869c3d3/attachment.htm>
More information about the RE-wrenches
mailing list