[RE-wrenches] Load or Line Side was Solar accumulation panel
William Miller
william at millersolar.com
Wed Jan 13 19:51:05 PST 2010
Carl:
You are correct. I had the exact argument with an inspector. Here is what
I did to make a convincing argument: I opened the disconnect and then
reached in and touched the load side contacts (inverter side) with my
fingers. I turned to the inspector and said, "Now it's your turn to touch
the line side." Case closed.
William Miller
At 05:17 PM 1/13/2010, you wrote:
>Wrenches,
>
>I just had an AHJ require me to switch the load and line connections
>on the fused AC disconnect which sits between the inverters (AC
>Combiner panel) and the point of utility connection. The inverter
>was connected on the LOAD side of the fused disconnect, and while the
>AHJ agreed this was the safest configuration, (when the disco is OFF
>the fuses are safe to remove) he insisted that the PV array should be
>connected to the LINE side of the disconnect since it is supplying
>power rather than acting as a LOAD. Any similar experience or
>arguments I can make based on the NEC which might help change the
>position of the AHJ next time round? I still believe our initial
>installation represents the safest configuration.
>
>Carl Adams
>SunRock Solar, LLC
>_