[RE-wrenches] Solar accumulation panel
Drake Chamberlin
drake.chamberlin at redwoodalliance.org
Wed Jan 13 09:58:45 PST 2010
P.S.
In many cases it would be necessary to use a fused AC disconnect to
stay within the inverter manufacturer's specifications.
At 12:53 PM 1/13/2010, you wrote:
>Here is a wild idea. If you look at the Enphase inverter systems,
>several inverters connect together in parallel before going to an
>overcurrent device.
>
>In all cases, the point of connection to a utility system must be at
>a dedicated breaker. If there were multiple string inverters that
>would connect to one breaker, why not just use a junction box,
>instead of a combiner panel? You could put in an AC disconnect for
>each inverter, if it didn't come with one.
>
>The wiring would need to be sized for the combined output of the
>multiple inverters, which in many cases wouldn't be an issue.
>
>Drake
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100113/0075a6af/attachment.htm>
More information about the RE-wrenches
mailing list