[RE-wrenches] strings of older solar panels
Joel Davidson
joel.davidson at sbcglobal.net
Thu Nov 19 07:36:58 PST 2009
David KatzHello Lee,
The Solarex MSX-64 module was on the CEC 2001 Tax Year List of Approved
Photovoltaic Modules for the Solar Energy System Credit. If anyone would
like a copy of the 2001 approved modules list, contact me off-list. Lee, in
your case it doesn't matter because you can't "grandfather" used modules for
a rebate.
Joel Davidson
----- Original Message -----
From: Bill Brooks
To: dkatz at aeesolar.com ; 'RE-wrenches'
Sent: Wednesday, November 18, 2009 9:07 PM
Subject: Re: [RE-wrenches] strings of older solar panels
Lee,
Your idea about 2 strings of 16 is fine on a Fronius IG2000. The voltage is
correct and the inverter power is more than sufficient. There is no
difference at all in the way module bypass diodes were done then (early
1990s) as now. You want to check the Voc of each module to make sure there
are no failures, but beyond that, everything else is the same. They are not
on the CEC list because they predate the list.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of David Katz
Sent: Wednesday, November 18, 2009 1:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] strings of older solar panels
Lee
I would be inclined to use groups of 4 modules wired for 24 volts connected
to an Enphase inverter. This will give you less problem with mismatch loss.
256 watts is high but they are probably a bit lower in output that that.
David
David Katz
Chief Technical Officer
AEE Solar
1155 Redway Drive
P.O. Box 339
Redway, CA 95560
Tel (707) 825-1200
Fax (707) 825-1202
dkatz at aeesolar.com
www.aeesolar.com
DISCLAIMER:
This communication, along with any documents, files or attachments, is
intended for the use of only the addressee and contains privileged and
confidential information. If you are not the intended recipient, you are
hereby notified that any dissemination, distribution or copying of any
information contained in or attached to this communication is strictly
prohibited. If you have received this message in error, please notify the
sender immediately by e-mail reply and destroy the original communication
and its attachments without reading, printing or saving in any manner.
Solar Plexus wrote:
Hi Wrenches.
I have a customer with 32 of the Solarex MSX-64 solar panels an a
battery-based system. He wants to go batteryless inverter. So I am looking
at 2 strings of 16 in series. But the solar panel spec sheet doesn't say
anything about system voltage rating. Can I do this?
If one solar panel in the string is shaded, does it see the full string
voltage of around 280 volts? Is there something in the way new panels are
made that makes them more able to handle this voltage, or is it just that
they are now tested for it?
My guess is this request may be happenning a fair amount. Is there a
reason these panels are not listed on the California GoSolr website?
Lee Tavenner
Solar Plexus
More information about the RE-wrenches
mailing list