[RE-wrenches] XW (was Outback "F"ware)
Nick Soleil
nicksoleilsolar at yahoo.com
Fri Oct 23 16:57:45 PDT 2009
Yes, but atleast the QOU breakers are din rail mounted and your electrical distributor can probably get them from Square D. The XW system is sweet. The XW monitor (on the Xanbus network), with the Dual AC inputs provides a superior monitoring/control system. The system is far cleaner than any other off-grid inverter system, and amazingly, the customer can understand the controller! Which makes all the difference to me.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
________________________________
From: Allan Sindelar <allan at positiveenergysolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Fri, October 23, 2009 12:56:37 PM
Subject: Re: [RE-wrenches] XW (was Outback "F"ware)
William,
The first time I saw a prototype
of the XW system I groaned at the use of QOU breakers. Partly it was for the
reason you mention, and partly because the QOU had become a white elephant, not
used in our industry since the demise of the APT/Trace Powercenters. QOUs aren’t
normally stocked at our local SqD distributor, so we would have to carry yet
another stock of breakers, besides OBDC and the CBI lines. My comments to the
Xantrex techies didn’t make any difference, either.
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP
Certified Photovoltaic Installer
EE98J
Journeyman Electrician
Positive
Energy, Inc.
3201 Calle
Marie
Santa Fe, New
Mexico 87507
505 424-1112
www.PositiveEnergySolar.com
Ray:
Here's one specific complaint: When using Flexware, each QOU breaker
needs a separate lead to the bus for feed. Too bad we can't have a bus
bar for plug on breakers.
…I emphasized that I would like to see
the AC KO a standard distance from the back plane to allow connection via
standard offset to an off-the-shelf load center. Never happened....
William Miller
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091023/43f90a2d/attachment-0004.html>
More information about the RE-wrenches
mailing list