William Miller william at millersolar.com
Wed Aug 19 20:09:00 PDT 2009


Don:

The DC feeder may have an AC component imposed on it by the switching in 
the inverter.  We installed a large Hawker battery bank 
(http://millersolar.com/Portfolio/Commercial/Cal_Trans/cal_trans_gorda.html) 
that physically vibrates under heavy charging.  We have also seen in this 
forum reports of RF interference from battery cables.

William Miller



At 06:07 PM 8/19/2009, you wrote:
>In a message dated 8/19/2009 2:42:48 P.M. Pacific Daylight Time, 
>daveclick at fsec.ucf.edu writes:
>>1. Running the positive and negative wires through separate conduit
>>violates 300.3, and could cause eddy currents in the combiner/disc boxes.
>
>
>No eddy currents with DC-- But not sure why all not run in single conduit.
>
>Don Loweburg