[RE-wrenches] utility line voltage issues

Steve Lawrence SteveL at thesolarcenter.com
Mon Aug 17 11:33:01 PDT 2009


I've run into this issue as well.  I always keep the inverters as close
to the main service panel as possible to minimize voltage problems on
the AC side.  The vast majority of AC voltage problems I have are when
the inverters are far away from the house, and even though the wire
might be oversized, breakers, bends, disconnects, etc all have a minimal
resitance which can add up and require a higher output voltage from the
inverter.

To reiteratate what Bill said, the inverters may say they work between
211-264V, but if you start digging deep into the manual, they have
slighty smaller windows.  I distinctly remember one job with two Xantrex
GT inverters on a line side tap, and the grid voltage coming in was
255V.  The utility company (Con Edison) said this was normal for them.
Occasionally, the grid would go up to 260V, and the Xantrex would kick
off.  It doesn't reconnect until it hits 254V, and the grid never got
down that low, so the client's inverter would be off all day long.
Xantrex gave me the software and password to change the limits to 264V
on the upper limit, and a reconnect voltage of 260V, which solved the
problem.  I've done this with Fronius inverters as well.

Steven Lawrence

------------------------------

Message: 3
Date: Mon, 17 Aug 2009 09:04:46 -0700
From: "Bill Brooks" <billbrooks7 at yahoo.com>
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] utility line voltage issues
Message-ID: <006d01ca1f54$728d0980$57a71c80$@com>
Content-Type: text/plain;	charset="us-ascii"

William and others,

The standard requirement in IEEE929 and IEEE1547 that is tested in
UL1741 is
+10%/-12%. Admittedly, some utilities, particularly in more rural areas,
may
get close to these limits at times. Just for a little history lesson
that
very few people know about, this happens to be a very hard fought and
won
battle. Initially when IEEE929 (the original PV interconnection
document)
was being written, utilities wanted inverters to trip at +/- 5%.
Realizing
that this would be a death blow to the PV industry, several of us worked
on
the justification for why that did not make sense. We finally won when a
key
utility engineer got on our side and the proper limits went into place.
The
standard also recognizes that special locations, like island grids
(Hawaii)
and other remote grid areas may need even wider ranges to handle typical
fluctuations. Widening voltage windows of the inverter requires utility
permission. 

The voltage limits we have now are good, but most people don't
understand
the rest of the story. As was mentioned in the post, most PV inverters
do
not trip at their actually limits, they typically trip a few percent
inside
those limits (+8%/-10%). This is due to the difficulty of measuring ac
voltage accurately, and the penalty within UL1741, the test standard, if
you
fail one of these limit tests. Since there is no penalty in the standard
for
tripping early, but a large penalty for tripping late, inverter
manufacturers constrain their limits so that they trip within the limits
every time, even if their transducers are at the maximum offset allowed.

That is why it is so important for installers to try to stay within 1%
voltage drop on the ac side. Since the utilities are allowed to go to
the
limits of +/-5% routinely (ANSI Range B), and outside that range for
"short"
periods of time (a few hours is short compared to 8760 hours), a 3%
voltage
drop will cause inverter tripping that is not the utility's fault--it is
the
installers fault.

I'm not defending the utilities, but having responded to dozens of
utility
voltage complaints, I can say that 80-90% of the complaints were the
installer's fault in having too high a voltage drop in their inverter
output
circuits. The legitimate issue is that PV inverters are one of the only
things on the residential utility system that reacts to bad voltage. We
are
now placing tens of thousands of voltage sensors on the utility grid,
and
they will find bad places. The key is to be part of the solution, not
part
of the problem--keep your ac voltage drop low. For every voltage drop
dollar
you spend on the dc side of your design, you should put $2 toward the ac
side voltage drop--it is at least twice as important because it may
determine whether or not the system runs.

Bill.

Bill Brooks, PE
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
Office and Mobile: 707-332-0761
Office Fax: 707-451-7739
email: Bill at BrookSolar.com
www.BrookSolar.com




-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Joel
Davidson
Sent: Sunday, August 16, 2009 1:48 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] utility line voltage issues

Correction: 4 KV

----- Original Message ----- 
From: "Joel Davidson" <joel.davidson at sbcglobal.net>
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Sent: Sunday, August 16, 2009 12:08 PM
Subject: Re: [RE-wrenches] utility line voltage issues


> Hello William,
>
> SCE has some 4kVA long, skinny feeders that get voltage sag during
high 
> usage periods (August afternoons air conditioning and December nights
xmas

> lights and heating). High grid voltage can occur in some areas when
SCE 
> increases the voltage to compensate for voltage sag. High grid voltage
can

> also occur when utility and/or customer wires are undersized.
>
> The CPUC, not lawyers, tell electric utilities to fix grid voltage 
> problems. You need to file a complaint with specific information to
the 
> CPUC. With no PV system on and using an rms meter, measure the
voltages. 
> Record the times and in what neighborhoods are you measure high or low

> voltage. Then file a written complaint to the CPUC (contact info on
the 
> back of an electric bill). The CPUC accept the complaint, investigate,
and

> tell SCE to correct the problem(s).
>
> If the grid voltage is within acceptable range and the grid-tie
inverter 
> is still shutting down, then leave the inverter off and measure grid 
> voltage at the inverter AC in. If voltage is high, pull the grid-tie 
> breaker and measure grid voltage. It should be within range. If not,
then 
> the wiring from the grid-tie breaker may be undersized or the inverter

> input voltage setting may be out of range.
>
> Joel Davidson
>
> ----- Original Message ----- 
> From: "William Korthof" <wkorthof at eesolar.com>
> To: <re-wrenches at lists.re-wrenches.org>
> Sent: Sunday, August 16, 2009 10:06 AM
> Subject: [RE-wrenches] utility line voltage issues
>
>
>> I'm beginning to wonder if the allowed voltage range for grid-tie 
>> inverters (+/-10%) is too
>> sensitive in some networks and contributes more harm than benefit.
This 
>> is close to home.
>>
>> Generally, the utility voltage at my house is in the mid 120's---
around

>> 125 vac per phase.
>> But at times, the voltage goes up higher---two weeks ago I saw 129 to

>> 130V per phase.
>> That voltage was high enough to put all of the inverters that I
checked 
>> offline for much
>> of the day.
>>
>> So I've had to call in "voltage trouble" complaints to the utility at

>> least a dozen times
>> over the past 5 years in response to seeing inverters offline and
line 
>> voltage about
>> 8% above nominal.



------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



End of RE-wrenches Digest, Vol 2, Issue 871
*******************************************



More information about the RE-wrenches mailing list