[RE-wrenches] solid vs stranded AC vs DC
Darryl Thayer
daryl_solar at yahoo.com
Wed Aug 5 06:34:31 PDT 2009
Thanks DAve yes I meant 2% more for stranded than the voltage drop for solid. So the number is very small. Your example was right on.
Darryl
--- On Wed, 8/5/09, Dave Click <daveclick at fsec.ucf.edu> wrote:
> From: Dave Click <daveclick at fsec.ucf.edu>
> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Wednesday, August 5, 2009, 7:58 AM
> 2% loss is significant, but I think
> that Darryl was saying that the
> resistance for stranded wire was 2% higher than solid. So
> if you had a
> 3% voltage drop in your system with stranded wire, you
> could rewire the
> system with solid wire and have a voltage drop of (3% x
> 0.98) 2.94% at
> peak production; that's less than 1 kWh/yr per kW
> installed.
>
> DKC
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] solid vs stranded AC vs
> DC
> From: Joel Davidson <joel.davidson at sbcglobal.net>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Date: 2009/8/3 20:31
>
> > 2% loss from any resistance source over 25 years is
> significant.
> >
> > ----- Original Message ----- From: "Darryl Thayer"
> <daryl_solar at yahoo.com>
> > To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> > Sent: Monday, August 03, 2009 2:04 PM
> > Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
> >
> >
> >
> > Yes, that is what the code book and my electricians
> handbook says, but
> > 2% is very little. I would think that passing
> through a conduit hole is
> > larger than that.
> > Darryl
> >
> > --- On Mon, 8/3/09, Matt Tritt <solarone at charter.net>
> wrote:
> >
> >> From: Matt Tritt <solarone at charter.net>
> >> Subject: Re: [RE-wrenches] solid vs stranded
> AC vs DC
> >> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> >> Date: Monday, August 3, 2009, 3:49 PM
> >>
> >>
> >>
> >>
> >>
> >>
> >> Darryl,
> >>
> >>
> >>
> >> Say what?! This would seem to indicate that solid
> core is
> >> actually
> >> better for DC than stranded wire. Can this
> possibly be
> >> true??
> >>
> >>
> >>
> >> Matt
> >>
> >>
> >>
> >> Darryl Thayer wrote:
> >>
> >> I looked in the code book and
> found stranded wire
> >> has about 2% higher DC resistance than solid,
> Chapter 9
> >> table 8, and that for AC resistance the same value
> as DC
> >> resistance to within the table accuracy Chapter 9
> Table 9
> >>
> >> This table points out that for AC resistance it
> is
> >> important to know the conduit system, as the
> reactance will
> >> have an effect. With AC it is important to
> never allow a
> >> single wire to pass through a metal surface as
> this will
> >> induce eddy currents and magnetic effects into the
> metal
> >> causing voltage drop and heating.
> >>
> >> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
> >> wrote:
> >>
> >>
> >>
> >> From: jay peltz <jay at asis.com>
> >> Subject: Re: [RE-wrenches] solid vs stranded
> AC vs DC
> >> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> >> Date: Friday, July 31, 2009, 10:01 PM
> >> Hi Darryl,
> >>
> >> But what are the differences and when do they come
> into
> >> play?
> >>
> >>
> >>
> >>
> >> On Jul 31, 2009, at 7:25 PM, Darryl Thayer wrote:
> >>
> >>
> >>
> >> Well there is very
> slight differences between AC
> >> and
> >>
> >>
> >> Dc But this
> >>
> >>
> >> difference
> >> is so slight that it has no effect on anything we
> will
> >>
> >>
> >> do.
> >>
> >>
> >> Darryl
> >> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
> >>
> >>
> >> wrote:
> >>
> >>
> >>
> >> From: jay
> peltz <jay at asis.com>
> >> Subject: [RE-wrenches] solid vs stranded AC
> >>
> >>
> >>
> >> vs DC
> >>
> >>
> >>
> >> To:
> "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> >> Date: Friday, July 31, 2009, 7:00 PM
> >> HI All,
> >>
> >> I'm trying to understand this wire issue.
> >>
> >> Whether or not there is a difference between
> >>
> >>
> >>
> >> stranded or
> >>
> >>
> >>
> >> solid wire
> for DC or AC.
> >>
> >> Any takers on this one?
> >>
> >> thanks,
> >>
> >> jay
> >>
> >> peltz power
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >>
> >>
> >>
> >>
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >>
> >>
> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >>
> >>
> >> No virus found in this incoming message.
> >> Checked by AVG - www.avg.com
> >> Version: 8.5.392 / Virus Database: 270.13.42/2279
> - Release
> >> Date: 08/03/09 05:57:00
> >>
> >>
> >>
> >>
> >>
> >>
> >> -----Inline Attachment Follows-----
> >>
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list