If I understand the issue correctly, the inspector is requiring the
PV disconnect for the utility feed to be treated as a service. By
the definition in Article 100, it can not be a service, and therefore
should not be subject to the rules of a service.
The definition is quoted below:
Service. The conductors and equipment for delivering electric energy
from the serving utility to the wiring system of the premises served.
The comment from the NEC Handbook is quoted below:
The definition of service includes the statement that electric energy
to a service can be supplied only by the serving utility. If electric
energy is supplied by other than the serving utility, the supplied
conductors and equipment are considered feeders, not a service.
Energy supplied by an inverter is not coming from a utility.
Drake
At 12:13 PM 3/15/2009, you wrote:
><I just found this sitting in my Drafts folder. Meant to send last week.>
>
>Hi Wayne,
>
>Grouping is a gray area in the NEC. Subject to the discretion and
>interpretation of the AHJ. Always has been since the concept of
>grouping was established. Certain conditions and occupancy
>classifications may allow different interpretations.
>
>Article 230 provides requirements for services. 230.2 Number of
>Services defines how many services are allowed to supply a building
>or structure. In general, only one is allowed unless one of several
>special conditions, occupancies, capacity requirements, or different
>characteristics are met. 230.2(A) Special Conditions stipulates that
>"Additional services shall be permitted to supply the following:"
>(1) Fire pumps; (2) Emergency systems; (3) Legally required standby
>systems; (4) Optional standby systems; (5) Parallel power production
>systems; and (6) Systems designed for connection to multiple sources
>of supply for the purpose of enhanced reliability. If you are doing
>a non-backup, grid-connected system, your application falls under
>230.2(A)(5) Parallel power production systems. This is important for
>a couple reasons, primarily because it specifically allows the
>second service in the first place. It is also important because, as
>a Parallel power production system, this is a Special Condition and
>not a "normal" service.
>
>Requirements for Service Equipment Disconnecting Means are found in
>Article 230 Section VI. Article 230.70 General specifies that "Means
>shall be provided to disconnect all conductors in a building or
>other structure from the service-entrance conductors." (Keep in mind
>that little word "in".) Article 230.70 then goes on to list
>additional requirements for this service disconnect... Readily
>Accessible outside or inside nearest the point of entry, not in
>bathrooms, readily accessible again, marked as service disconnect,
>and suitable for use.
>
>Article 230.71 defines the Maximum Number of Disconnects. 230.71
>says that the service disconnecting means for each service permitted
>by 230.2 shall not consist of more than 6 switches or breakers... In
>a single enclosure, group of separate enclosures, or switchboard.
>There also shall not be more than 6 sets of disconnects grouped at
>any one location.
>
>Article 230.72 gives us the Grouping concept. 230.72(A) General
>says, "The two to six disconnects as permitted in 230.71 shall be
>grouped. Each disconnect shall be marked to indicate the load
>served." There is NOT a definition of "grouped".
>
>230.72(B) Additional Service Disconnecting Means specifies that the
>service disconnect for all of the Special Conditions listed in
>230.2(A)(1) through 230.2(A)(4) "shall be installed remote from the
>one to six service disconnecting means for normal service to
>minimize the possibility of simultaneous interruption of supply."
>There is no direct mention of 230.2(A)(5) Parallel power production
>systems. It is unclear to me if this is intentional or
>unintentional. What is clear to me is that, if for no other reason
>than the 230.2(A) Special Conditions classification, it is not part
>of the "normal service".
>
>The explanation in the NEC Handbook (2008) says: The intent of
>230.2(A) is to permit separate services, where necessary, for fire
>pumps (with one to six disconnects) or for emergency, legally
>required standby, or optional standby systems (with one to six
>disconnects), in addition to the one to six disconnects for the
>normal building service. Article 230 recognizes that a disruption of
>the normal building service should not disconnect the fire pump,
>emergency system, or other exempted systems. Because these services
>are in addition to the normal services, the one to six disconnects
>allowed for them are not included as one of the six disconnects for
>the normal supply. These separate services are permitted by 230.2
>and are required to be installed in accordance with all the
>applicable requirements of Article 230.
>
>Notice that the explanation reiterates the "one to six disconnects"
>per service principle. What is more important is the concept of
>"remote from the normal service disconnecting means for the purpose
>of reliability".
>
>A couple of very important elements of the justification for
>FIT-subsidized DG PV are grid reliability and homeland security. In
>fact, the location of the DG disconnect in this case should be at
>the discretion of the interconnecting utility. This is generation,
>directly to and on behalf of the serving utility. Generation is
>treated differently than loads by grid operators and rightfully so.
>In the case of most utility distribution maps, meter locations for
>loads are mapped whereas generator disconnects are mapped. Note
>that, unless the customer's meter and service disconnecting means
>are located adjacent to or grouped with one another, the utility
>doesn't map (or even care) where the service disconnect is
>physically located. When you add generation, whether it's
>utility-side or customer-side connected, they map the generator
>disconnect. Quite different scenarios. There are fundamental
>differences between the need and use of each on the part of a utility operator.
>
>In utility-side configurations, the generator is 100% electrically
>isolated from and independent of the "normal" service. Their
>respective service disconnects should NOT be "required" to be
>located adjacent to or grouped with the other. Depending on the
>actual conditions and arrangements at the site, it may be prudent to
>provide a permanent placard at each service disconnect showing the
>location of the other.
>
>Personally, assuming otherwise "normal" conditions and
>appropriateness of the existing premise electrical system, I would
>present the AHJ with this rationale and explanation. It may even be
>prudent to have an earnest conversation with the local utility and
>see if they are willing to support this position.
>
>Try to find a line-crew somewhere and talk with them about it. Tell
>them that the local AHJ is trying to make you put the generator
>disconnect inside the house, next to the existing service
>disconnect. (This is one of the options the AHJ is presenting you
>with.) You will get one of two responses... If the person or crew
>you are speaking with has a jaw full of chew, you will most likely
>get a macho response like, "Shoot. That dinky solar system ain't
>gonna hurt us no-how. <spit> We just throw a chain over the line and
>take it to ground 'til we're done clearing the line. <spit> If your
>generator ain't ready when we pull the chain, then too bad for you."
>The other response you will get goes something like this: "They
>wanna what? Don't they know we don't wanna have to bust down
>somebody's door to have to lockout the generation? Man, it's our
>lives at stake out here. Who is this idiot building inspector?" You
>are far more likely to get the second response from a lone lineman.
>For some reason, when they are in groups, the macho comes out. I've
>had this conversation with these guys a few times over the years.
>For various reasons. It's funny to watch the whole group go from
>macho to pissed off when one of them says, "Wait a minute... He's
>right. That building inspector don't know what he's talking about.
>The customer's load don't have nothing to do with the generation...
>Generation is our business."
>
>Thought I'd pass it along.
>
>Matt Lafferty
>Solar Janitor
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Wayne Irwin
>Sent: Wednesday, March 11, 2009 7:56 AM
>To: re-wrenches at lists.re-wrenches.org
>Subject: Re: [RE-wrenches] Line Side Feed In and Disconnects
>
>Wrenches,
>
>They are requiring us to install two service disco's. One for the PV
>(between the PV and the FIT (payment) meter) and one for the house
>(between the distribution panel and the standard utility (billing)
>meter). As Darryl stated, the reason is so that they are grouped
>together. They said it did not necessarily matter wether or not they
>were grouped inside or outside, so long as they are grouped.
>We normally install (batteryless) grid tie systems outside with
>discos within 10' of the utility meter. So as I see it, we must
>either install the inverter and PV disconnect inside next to the
>distribution panel, or install an additional disco outside between
>the house panel and the utility meter, next to the inveter, AC
>disconnect and FIT meter.
>
>Wayne Irwin
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org