[RE-wrenches] Strings and series of batteries with reversereturn linkup
R Ray Walters
ray at solarray.com
Mon Dec 7 11:59:00 PST 2009
This is an excellent point that Jamie is making here. On electric vehicles, we do see up to 156 vdc series strings, and even with just a single string at 48 vdc, the separate cells are not being charged equally.
Current is equal, but not the voltage across each cell.
It's alarming to see some batteries (especially sealed ones) going way over charge, while others are undercharged. The controller only sees that the total voltage is at full charge, and then shuts off. I've pulled individual batteries out to charge separately. I think we really need smarter charging systems (similar to Li ion) that shutoff individual batteries or small groups to allow others to fully charge without overcharging others.
Just imagine seeing a new expensive sealed 12 v battery hitting 16.5 v, while others are still below 13.5v. It'll make you sick to your stomach, hearing it gas, when it's not supposed to.
HIgher charge currents make the problem worse.
Here's a regulator from Manzanita Micro that can do it:
http://www.manzanitamicro.com/index.php?page=shop.product_details&flypage=flypage.tpl&product_id=46&category_id=17&option=com_virtuemart&Itemid=64
I've worked with Rich Rudman there for years; he's very knowledgeable and good to work with. It might be a good idea, especially on large sealed batteries.
R. Walters
ray at solarray.com
Solar Engineer
On Dec 7, 2009, at 12:21 PM, James Surrette wrote:
> Hi Darryl,
>
> To further on your comments (I hope);
>
> One thing we've noticed that is an often overlooked (potential) problem. Even with a simple series sting (6, 12, 24 cells), the individual cell voltages are never identical - meaning initial charge acceptance is never identical. When you initially "activate" or "commission" a bank, assuming 48VDC you begin to charge at 57.5-60V. The overall voltage is attained relatively quickly but the individual cell voltages can be shockingly different (2.2 - 2.7V). The commissioning is complete when all cell voltages "balance" to the charging voltage, i.e. 2.4V. As series voltages increase (120VDC+) or multiple banks are used, the initial commissioning becomes increasingly more important as overcoming imbalance within the bank become more difficult. The most efficient commissioning occurs when low current is applied (2% of 20hr) until cells balance. The point to the comment, you might get away without balancing / commissioning / activating a series string but is imperative if using multiple parallel banks.
>
> Regards,
>
> Jamie
>
> >>> Darryl Thayer <daryl_solar at yahoo.com> 12/5/2009 9:31 PM >>>
> This also assumes all the identical batteries are at identical temperature, and it one is slightly warmer or can not lose heat as fast, if being charged it will get warmer. the warmer battery will do what? have a lower vltage, have higher current and receive more heat, and get warmer, this is significant. I have never seen a battery set tha all batteries have the same thermal conductance to ambient
> Darryl
>
> --- On Sat, 12/5/09, boB Gudgel <boB at midnitesolar.com> wrote:
>
> > From: boB Gudgel <boB at midnitesolar.com>
> > Subject: Re: [RE-wrenches] Strings and series of batteries with reverse return linkup
> > To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> > Date: Saturday, December 5, 2009, 3:45 PM
> > Antony Tersol wrote:
> > > Assume 3 parallel battery stings, with identical
> > batteries of internal resistance r.
> > >
> > > Assume identical wire leads of resistance R.
> > >
> > > Then when the batteries have the same state of charge
> > and their internal resistances are equal, one can solve for
> > the current in each string.
> > >
> > > I1 = I3
> > > I2 = I1 r / (r+R)
> > >
> > > where I2 is charging current thru the middle string.
> > >
> > > The amount that the middle current is reduced is a
> > function of the relative sizes of the wire and battery
> > resistances.
> > >
> > > For R << r, I2 --> I1.
> > > For r << R, I2 --> 0.
> > >
> > > With a buss bar arrangement, I1 = I2 = I3 = V/(2R +
> > r)
> >
> > One thing this does not take into account though, is the
> > inductance of all the wires brought
> > on by the wire lengths and their loop area, which in a
> > usual inverter with ripple current, will also limit the
> > current
> > through the system... That will also have
> > some undesired consequences with the voltages
> > seen at the inverter terminals due to resonances, etc.
> >
> > In ~can~ be significant.
> >
> > boB
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content.
>
> The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091207/9b5e06f4/attachment-0003.html>
More information about the RE-wrenches
mailing list